Dear All,
This is Senthil Kumar. I came across a serious concern on a recent PHA study done for one of our new compressors on site.
Service- Hydrogen gas
Inlet- 125 psig
outlet 600 psig
Compressor- 3 stage, Reciprocating type
I was not sure about the relief design of this compressor. I raised the question on protection devices for this equipment and found that the suction side of the compressor doesn't have a relief valve .
I talked to the Project engineers. They considered the first stage relief valve (Set 300# sized for blocked outlet case) to take care of the whole suction side.
Mechanical Engineers considered that there is no obstruction to this relief valve from the inlet. I'm still concerned that the check valve in the Suction/Discharge drums (8 Nos.) can stick in closed position to block the whole inlet to the relief and cause serious explosion/damage.
What are all your thoughts on this? Can i consider that nothing can obstruct the flow path to this relief valve? (see the attached drawing for a basic flow scheme)
I have no idea how to make sure that the suction/discharge drums will not stick closed.
I'm trying to justify to have a relief at the suction line upstream of the suction drum to protect the system in case the discharge relief opens and pressurises the suction.
Please help me on this.