Partial Pressure Question
#1 Steve Hall
Steve Hall
  • 167 posts
Posted 22 August 2013 - 12:02 PM
Imagine an indoor space with a slightly permeable wall separating it from the outside (leaking windows, for example). The indoor space has humidity and pressure control, so it is 10 Pa positive relative to the outside, and the dew point is roughly 17C. This makes the partial pressure of the water vapor approximately 2 kPa.
A colleague asserts that if the outdoor dew point is 22C, so the partial pressure of the water vapor is approximately 2.6 kPa, that water will penetrate into the indoor space even though the total pressure is higher indoors.
Do you agree?
#2 PingPong
PingPong
  • 1,473 posts
Posted 22 August 2013 - 12:37 PM
Yes, I agree with your colleague. It is only partial pressure of diffusing component that matters.
Note that in your attachment you interchanged the Total Pressure numbers.
#3 Steve Hall
Steve Hall
  • 167 posts
Posted 22 August 2013 - 12:57 PM
Yes, I interchanged the total pressure numbers.
Thanks. So is it a diffusive process since air will continuously flow from indoors to outdoors?
#4 PingPong
PingPong
  • 1,473 posts
Posted 22 August 2013 - 03:59 PM
It is a diffusive process, but any air flow has no influence on the direction of H2O ttransport.
If the wall is only permeable for H2O , but not for N2 or O2 . there will still be transport of H2O from its higher to its lower partial pressure.
Strictly speaking it is the fugacity of the H2O vapor that drives the diffusion until equilibrium between both spaces is achieved. As we can consider atmospheric air inside and outside to be ideal gases, fugacity equals partial pressure for each component i in the gas mixtures.
#5 Steve Hall
Steve Hall
  • 167 posts
Posted 23 August 2013 - 05:52 AM
Great. Thanks!