Our Propane refrigeration system equipped with fin fan coolers to condense propane vapors. We are facing difficulties to remove moisture content from these exchangers after doing hydro testing during our major shutdown. This moisture content creates plugging in low temp chillers when unit started back. Even we observed free water content in the low point area which takes lot of time to remove from the system. Each fin-fan exchanger purged with dried Inst air followed by nitrogen but it is difficult to remove moisture content with low volume of available air/nitrogen. Purging with large amount of warm fuel gas reduced moisture content but it consume lot of man-hour to complete the process which delays startup process still, we could not reduce the moisture content to minimum requirement . Dry out method by vacuum pulling need to be confirmed as these exchangers not designed for negative pressure.
Please advise best alternative method to carryout pressure test for these exchangers and kindly suggest if any method to remove this moisture content effectively.
Note: Propane refrigeration system equipped with large number of bays and design pressure of bay 26 bar/temp 110 deg C