I don't think the redesign will help - with regards to condensation on the flue gas side. Feed water inlet temperature is too low and it wil always cause localized sub-cooling (and condensation) in the area of the exchanger where water starts to exchange heat with the flue gas. This phenomenon is known for all air/flue gas and water/flue gas preheaters.
What needs to be done, is to raise the temperature of feed water beyond the dew point of flue gas. If flue gas contains SOx, severe corrosion and plugging of economizer tubes occurs. See attached article, and the dew point calculator.
http://users6.jabry....athy/dewpta.asp