A wet cooling tower is just a simple column (with a few theoretical stages) with the warm (328 K) water entering at the top and the cooling air (308 K) entering at the bottom. Should be easy to simulate that in Hysys, or any other simulator.
The cooled water leaving the bottom of the cooling tower can never become colder than the adiabatic saturation temperature (wet bulb temperature) of thye entering cooling air. In actual practice the cooled water is usually about 2 - 3 oC warmer than that, so in your case expect 302 - 303 K.
Okey, thank you for your help! I see that I have been a bit misleading when it comes to the temperature.
Anyways, can you help me simulate a wet cooling tower? I cant make it to work. So my "correct" data is:
Air temperature = 35 C
Air humidity = 55 %
These two parameters give me an wet bulb temp on 27 C and a dew point temp on 25C
The warm water comes in to the tower with a temperature of 45 C. I want to cool it down as low as possible, which I understand is to 30C,(2-3 degrees higher than the wet bulb temperature.). The mass flow is 400000 kg/h
Okey, so the air entering the tower contains a bit of water vapor, because of the humidity, right? So to take advantage of this, would I want to cool down the air before it enters the tower? Cool it down to the dew point temperature?
In addition, I guess I need some make up water, since the tower uses evaporation of water as cooling method. Where do I add this? I ampretty new to Hysys, so I'm having a hard time figuring this out, so I would really appreciate it if someone could help me.