Dear All;
Please, there are two amine Pumps, one ( P-101A) is running and One (P-101B) is in standby mode, and each pump has it's own lube oil cycle (Lube oil System is completely separated).
And functional specification from vendor shown that:
If the pump is in standby mode, the relative auxiliary lube oil system shall be always ready.
Now,
for the logic of the pump, there is a pressure transmitter PT for the oil cycle for each pump, this pressure transmitter trip the pump when the pressure of oil cycle become Law Law.
BUT, Shall I make this transmitter PT, trip both pumps, I mean If P-101A is running and P-101B is in standby , and PT for P-101B (standby one not running) become low low, shall this transmitter trip the running pump P-101A ?
Note that: there is a FAL (flow transmitter) on discharge line of the pump , in case of law flow will trip the running pump and start the standby one automaticaly.
Thanks;
Shahin.