I have a few questions pertaining to relief valves and their nameplates.
1) Found a conventional relief valve that had a set pressure change. On the original nameplate, the following items were crossed out: set pressure, capacity, and CDTP. There is constant superimposed back pressure (greater than 10% of set pressure) in the discharge line, so the CDTP is different than the set pressure. There was a secondary tag attached to the valve that listed the new set pressure and capacity, but did not have the new CDTP listed. Should the secondary valve state the CDTP?
2) Found a relief valve with a missing nameplate. It can't be 100% verified; the valve should be replaced?
3) Found a valve that looks like the original nameplate fell off and a new one was put on (has service provider's name listed on it instead of the manufacturer's). The nameplate is no longer code stamped (UV and NB); the valve should be replaced?
4) Sort of related, how does the NBIC "VR" program play into valve servicing? My understanding is that if any machining or part replacement needs to be done, a tag stamped VR needs to be present? For example, my question 1), if a set pressure change was performed and then a CDTP correction needed to be performed, would this then need a VR stamp? My thinking is that the spring would have to be replaced.
I appreciate your help.