Is This A Credible Release Scenario?
9 replies to this topic
#1 chemks2012
chemks2012
  • 195 posts
Posted 04 June 2014 - 06:45 AM
Hello all,
Please find the attached simple sketch.
I am sizing RV01 and wish to consider one of this scenarios please but not sure if this is a credible scenario and I want your opinion.
The reactor jacket is supplied with low pressure steam at 2barg.
Relief valve set pressure is 6barg
Jacket design pressure is 7barg
If control valve [CV01] fails and AV04 is closed as well as jacket inlet is blocked – the steam flow through failed control valve would be 1000kg/hr steam. Do you think RV01 will be activated at all as the steam pressure is 2barg?
I am bit confused and I need your help.
Edited by chemks2012, 04 June 2014 - 06:49 AM.
#2 fallah
  • 5,026 posts
Posted 04 June 2014 - 06:47 AM
Nothing attached...!
#3 chemks2012
chemks2012
  • 195 posts
Posted 04 June 2014 - 06:50 AM
Hi Fallah,
Can you download the attachement now?
#4 fallah
  • 5,026 posts
Posted 04 June 2014 - 06:52 AM
Yes, thanks...
#5 fallah
  • 5,026 posts
Posted 04 June 2014 - 07:03 AM
Is the CV01 full open in failure position? At the same time what are the AV03 and AV02 situations? Is the steam pressure source 2 barg or this pressure is after CV01 in normal condition?
#6 chemks2012
chemks2012
  • 195 posts
Posted 04 June 2014 - 07:11 AM
Hi Fallah,
Supplier confirmed when CV01 is 100% open it will pass 500kg/hr. I applied safety factor of 2 giving 1000kg/hr.
When steam is supplied, all valves will be closed except AV02.
Steam is supplied from a boiler which is locally protected by a relief valve at 2.5barg.
Yes, pressure drop through CV01 is 0.5bar when it is 100%. So let's say pressure at the CV01 downstream would be 1.5barg.
#7 fallah
  • 5,026 posts
Posted 04 June 2014 - 07:19 AM   Best Answer
No, this cannot be a credible scenario to overpressure the steam jacket with design pressure of 7 barg...
#8 chemks2012
chemks2012
  • 195 posts
Posted 04 June 2014 - 07:20 AM
Thanks Fallah,
But I am just wondering what will happen to the blocked steam in that situation?
#9 fallah
  • 5,026 posts
Posted 04 June 2014 - 07:38 AM
If during CV01 failure the AV02 isn't closed, the steam isn't blocked. If AV02 is closed, the steam is blocked in the jacket with a pressure of 2 barg. Then...2 barg LP steam in a jacket with DP of 7 barg...appears nothing happens other than after a while having a flooded jacket with the steam condensate...and a reactor that cannot absorb adequate heat to do the reaction at proper rate...!
Edited by fallah, 04 June 2014 - 07:39 AM.
#10 chemks2012
chemks2012
  • 195 posts
Posted 04 June 2014 - 07:52 AM
Thanks Fallah..
I believe, even if I consider that all the valves are closed, CV01 fully opens and the jacket nozzle itself is blocked [i.e. not letting steam flow in], steam will just condensate and hammering may occur but it will not cause a relief scenario?