I am working on cryogenic relief valve system currently. So far I understand that if you have a cryogenic liquid in a pipe system, the flow rate is based on heat leak input and heat of vaporization, since its a saturated liquid. So, Compressed Gas Association (CGA) has its on relief sizing standards.
I am confused with which of these will be applicable to a vacuum jacketed pipe relief valve sizing?
S-1.1 Pressure Device Standards Part 1 (circular cross-sectional storage units)
S-1.2 Pressure Relief Device Standards Part 2 (cargo and transportable)
S-1.3 Pressure Relief Device Standards Part 3 (permanently mounted units).
Is it S-1.1 (because pipe is like a cylinder) or S-1.3.?
Also, looking at the S-1.1 standards... they just calculate the orifice area calc based on the area of cylinder and sqrt of set point. Your calculated flow rate from heat leak and heat of vaporization is not being used.?
Also if you were to use API standards, the Thermal Hydraulic (blocked in line ) case doesn't really apply to this scenario because its a saturated liquid, it more closely resembles the fire case per API 520.
So if you do have your calculated flow rate , which API equation would you use to size the relief valve.
Thanks!
I also understand that thermal relief valve size is going to be very small. Hell, I don't even need to calculate it and can assign the smallest orifice but it would be nice to know how to define and solve the problem correctly and also understand which API 520 or CGA equation applies. Also, if one were to use a API 520 equations for cryogenics..is it considered wrong from legal stand point.
Edited by ChemE2014, 05 October 2014 - 12:05 PM.