Make the bypass (globe) valve no larger than the control valve.
NU UH!
Why do you need a bypass valve?
The very obvious answer is "so you can work on the control valve while the system is still in use".
In practice a bypass is often used under .... special conditions (such as during startup) so you want a
bigger bypass valve (unless you are
certain that twice the control valve capacity will always suffice) to quickly drain the system - which would be full of cold condensate.
A secondary consideration is that usually the bypass is located under the control valve; any fouling tends to collect down there and when you have a small bypass the accumulated stuff will very probably clog your bypass up (see the picture). Even in the cleanest systems some fouling occurs!
deposits.bmp 8.5KB
110 downloadsThe obvious addition I'd make to the design then would be to add a drain just before the bypass valve and to use that drain from time to time to flush out such deposits.