57 downloadsI'm part of a team that is reviewing the existing Safety Relief systems on our plant, based on tightening rules which require us to assume:
a) no operator intervention in the first 30 minutes
no credit should be taken for favorable instrument response (4.4.8.2 of API 521)
c) assume bypass valves are open,
etc.
We have an engineering firm on contract to calculate the required and available capacities for the enlarged group of scenarios and one 'class' of scenarios is baffling to us. I'll do my best to describe it, but you'll probably have to refer to the attached sketch to better understand. I'll check back in regularly in case you have questions.
- LIC-10 fails open. Even without the bypass open this still:
- fills the degasser vessel in just over 2 minutes (get to assume continued liquid outflow to G-8s).
- the PSV capacity is sufficient for this liquid relief (~ 33 usgpm).
- In ~11.8 minutes, the Cold HP Separator empties (even with continued inflow) and the gas (really 2 phase, but mostly gas) reaches the LIC-10 control valve.
- Once the gas passes the LIC, we are told that it expands/accelerates, rapidly increasing the pressure on the downstream piping/equipment, and driving very high relief rate requirements. In this case the contractor is indicating that we need > 140 in2 of orifice area (we currently have 3 in2 installed).
We have a conference call booked with the contractor to 'double check,' but directionally I can already get my head around the requirement (though the exact magnitude may change). We have four HP hydrotreaters with these issues (it is coming up on the Amine Flash Drum as well), so several circumstances where this issue is appearing. I'm hopeful that I don't have to recommend installation of a combined 780+ in2 of PSV capacity in the plant - it might be my last chance to make recommendations ;-)
Has anyone else been through a similar experience?
Did you encounter a similar huge jump in required capacity in similar services?
Did you come up with any ingenious methods to meet code? We've been talking about all kinds of things (RDs, buckling pin devices, increasing drum sizes - substantially - to ensure a vapor space remains, SIL level equipment on the upstream drum/control valves, .....) but nothing seems particularly cost effective yet.
Any assistance/advice will be greatly appreciated.