Loss Of Water In The Cooling Tower System
#1
Posted 01 June 2016 - 04:12 AM
#2
Posted 01 June 2016 - 04:56 AM
There is a loss of water in the cooling towers during the day when temperatures are high. Refilling the water system is not possible. Water cools a heat exchanger. There are three pumps to circulate the water and two cooling towers. The cooling system keeps the temperature at the heat exchanger output constant.I am interested if the shutting down a pump and increasing the fan speed will reduce water losses?Or maybe to turn on one more pump and reduce fan speed?Currently working with one or two pumps, and two cooling towers.
jtodic,
In a wet cooling tower system, the cooling capability is limited by local wet bulb temperature and approach. Then, if your existing cooling tower had been designed and optimized properly the only way to compensate the water loss is providing make-up water and system variables (fan speed, circulation velocity,...) changes nothing to do with improvement in system's cooling capacity...
#3
Posted 01 June 2016 - 06:57 AM
Hi jtodic,
What you call loss is normal evaporation unless you got loss through the louvers (drift) or an excess of blowdown .
Refer to the docs attached.
good luck.
Breizh
#4
Posted 06 July 2016 - 04:03 PM
The loss of water is mainly due to e a portion phenomenon in the coolIng tower.
The cooling power of the tower is directly linked to this evaporation.
Marc Jaouen.
@Breizh where are you located ?
Similar Topics
Pem Water ElectrolysisStarted by Guest_tomr91_* , 29 Jul 2025 |
|
![]() |
||
Triethylene Glycol (Teg) Regeneration SystemStarted by Guest_guoyinyanliner_* , 23 Jul 2025 |
|
![]() |
||
![]() Heat Loss Calculation From Cylindrical Tan;Started by Guest_rasprocess2026_* , 23 Jul 2025 |
|
![]() |
||
Psv For Refrigeration SystemStarted by Guest_runnerup_* , 30 Jun 2025 |
|
![]() |
||
![]() Guidance On Sizing Jacketed Pipe For Glycerine CoolingStarted by Guest_Kentucky08_* , 28 Jun 2025 |
|
![]() |