What is selection criteria and advantage of a Pilot-Operated Pressure Relief Valve over conventional Pressure Relief Valve?
|

Pilot-Operated Relief Valve
#1
Posted 06 June 2016 - 01:46 AM
#2
Posted 06 June 2016 - 02:03 AM
What is selection criteria and advantage of a Pilot-Operated Pressure Relief Valve over conventional Pressure Relief Valve?
lilwa,
Criteria for POSV selection:
1) When inlet line pressure loss exceeds 3% of the set pressure
2) When near to zero leakage is required
3) In the cases with high back pressure
4) In the cases with high capacity and high back pressure
5) When the difference between maximum operating pressure and set pressure is lower than %10 of the set pressure
Some advantages of pilot operated PSV over conventional one in brief:
1) Full lift at zero overpressure available
2) Capability to withstand higher built-up back pressures
3) Better seat tightness before relieving and after reseating
4) Possibility of in-line maintenance of the main valve
5) Capability of the remote pressure sensing
6) Higher set pressures available
7) No dependence of opening pressure to superimposed back pressure
8) Possibility of close operating pressure to set pressure
Edited by fallah, 06 June 2016 - 03:17 AM.
#3
Posted 08 June 2016 - 12:38 AM
What is selection criteria and advantage of a Pilot-Operated Pressure Relief Valve over conventional Pressure Relief Valve?
lilwa,
Criteria for POSV selection:
1) When inlet line pressure loss exceeds 3% of the set pressure
2) When near to zero leakage is required
3) In the cases with high back pressure
4) In the cases with high capacity and high back pressure
5) When the difference between maximum operating pressure and set pressure is lower than %10 of the set pressure
Some advantages of pilot operated PSV over conventional one in brief:
1) Full lift at zero overpressure available
2) Capability to withstand higher built-up back pressures
3) Better seat tightness before relieving and after reseating
4) Possibility of in-line maintenance of the main valve
5) Capability of the remote pressure sensing
6) Higher set pressures available
7) No dependence of opening pressure to superimposed back pressure
8) Possibility of close operating pressure to set pressure
Thank you Fallah!
I also need help in this perspective.
I have been trying to get idea about reverse current tripping of compressor/motor and mostly got electrical data mostly related to generators. I need to understand what is Reverse Power Tripping of a Compressor/Motor in process perspective. I am dealing with heavy duty multi-stage centrifugal process air (200 tonnes/hr) compressor feeding to a reactor.
Similar Topics
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Check Valve FailureStarted by Guest_Falah_* , 26 Mar 2025 |
|
![]() |
||
Multiport Selector Valve (Msv)Started by Guest__1angelia23_* , 12 Mar 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |
||
![]() Valve Cv InputsStarted by Guest_QuantumEng_* , 01 Apr 2024 |
|
![]() |