Hello Dear friends,
I have got a problem with vacuum pressure transmitter. The pressure transmitter near the ejector of distillation tower is always fluctuating, while on the downstream of this PT there isn't any fluctuations. The pressure produced by afore-mentioned ejector is around 2 KPa. The pressure on top and bottom of the vacuum distillation tower is 8 and 14 KPa respectively.
|

Vacuum Pressure Transmitter
Started by ali, Jun 27 2006 02:46 PM
3 replies to this topic
Share this topic:
#1
Posted 27 June 2006 - 02:46 PM
#2
Posted 27 June 2006 - 05:12 PM
Ali,
Ypu must pay careful attention to the details of how the instrument is hooked up. When measuring such low pressures, any small interference will be significant relative to your measurement. What I would be most concerned with is moisture. If there are any spots in the impulse line (the tubing between your column's overhead line and your transmitter) where moisture can accumulate, a significant error can be generated. Even if the impulse line slopes continuously from the transmitter to your process, which it should do, if the diameter is too small then small slugs of water could accumulate and invalidate your readings. This would be due to the water's surface tension. I cannot comment on the short term fluctuations you are experiencing. If you think they may be real, contact the vendor of the ejectors to resolve.
Good luck,
Doug
Ypu must pay careful attention to the details of how the instrument is hooked up. When measuring such low pressures, any small interference will be significant relative to your measurement. What I would be most concerned with is moisture. If there are any spots in the impulse line (the tubing between your column's overhead line and your transmitter) where moisture can accumulate, a significant error can be generated. Even if the impulse line slopes continuously from the transmitter to your process, which it should do, if the diameter is too small then small slugs of water could accumulate and invalidate your readings. This would be due to the water's surface tension. I cannot comment on the short term fluctuations you are experiencing. If you think they may be real, contact the vendor of the ejectors to resolve.
Good luck,
Doug
#3
Posted 03 July 2006 - 12:25 PM
QUOTE (djack77494 @ Jun 27 2006, 05:12 PM) <{POST_SNAPBACK}>
Ali,
Ypu must pay careful attention to the details of how the instrument is hooked up. When measuring such low pressures, any small interference will be significant relative to your measurement. What I would be most concerned with is moisture. If there are any spots in the impulse line (the tubing between your column's overhead line and your transmitter) where moisture can accumulate, a significant error can be generated. Even if the impulse line slopes continuously from the transmitter to your process, which it should do, if the diameter is too small then small slugs of water could accumulate and invalidate your readings. This would be due to the water's surface tension. I cannot comment on the short term fluctuations you are experiencing. If you think they may be real, contact the vendor of the ejectors to resolve.
Good luck,
Doug
Ypu must pay careful attention to the details of how the instrument is hooked up. When measuring such low pressures, any small interference will be significant relative to your measurement. What I would be most concerned with is moisture. If there are any spots in the impulse line (the tubing between your column's overhead line and your transmitter) where moisture can accumulate, a significant error can be generated. Even if the impulse line slopes continuously from the transmitter to your process, which it should do, if the diameter is too small then small slugs of water could accumulate and invalidate your readings. This would be due to the water's surface tension. I cannot comment on the short term fluctuations you are experiencing. If you think they may be real, contact the vendor of the ejectors to resolve.
Good luck,
Doug
Hi Dear Friend,
I appreciate your reply. I have to added that there is still another problem I have overlooked. The pressure observed adjacent to the ejector is usually more than the pressure away from ejector.
thanks
#4
Posted 04 July 2006 - 10:27 AM
Dear Ali
Steam jet ejectors are static equipments.
If you disconnect the ejectors from the systems and test them, and even this way the suction pressure fluctuates, it may be a motive steam problem (motive steam pressure is going up and down) or a cooling water problem ( more or less water, affecting the condensation temperature and at the end the suction pressure).
Regarding the motive steam, you should also check if the orifice nozzle is not clogged.
Hope this helps.
Regards
Paulo
Steam jet ejectors are static equipments.
If you disconnect the ejectors from the systems and test them, and even this way the suction pressure fluctuates, it may be a motive steam problem (motive steam pressure is going up and down) or a cooling water problem ( more or less water, affecting the condensation temperature and at the end the suction pressure).
Regarding the motive steam, you should also check if the orifice nozzle is not clogged.
Hope this helps.
Regards
Paulo
Similar Topics
Steam Pressure In Heat ExchangerStarted by Guest_mvanrijnbach_* , 15 Apr 2025 |
|
![]() |
||
Critical Pressure For Choke Valve SizingStarted by Guest_Sherif Morsi_* , 07 Nov 2017 |
|
![]() |
||
Vacuum RecoveryStarted by Guest_Paper_* , 25 Feb 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |
||
Pressure Of An Isolated Flow In PipeStarted by Guest_phoroogh_* , 30 Jan 2025 |
|
![]() |