Pump Pressure In Generator Closed Loop Cooling System
#1 kakil
kakil
Posted 11 October 2016 - 06:29 AM
centerfuge water pump in closed cooling system with below charstisitcs:
Q=200M3/hr
head=35m
but in working state the suction pressure is 3.5 bar and the discharge is 5.5bar
isit correct this state?
#2 fallah
  • 5,019 posts
Posted 11 October 2016 - 08:49 AM
Q=200M3/hr
head=35m
Kakil,
With lack of adequate info (pressure losses, elevations,...) it could be correct...!
#3 samayaraj
samayaraj
  • 239 posts
Posted 11 October 2016 - 12:21 PM
Since it is a closed loop, it will have expansion tank connected to the suction of pump. Expansion tank operating pressure may be higher ( may be 3.5 to 4 barg). Is your loop is hot water generator? Since as you said water, it will be pressurized to maintain in liquid state at elevated temperature. As Mr. Fallah stated, we need more information in order to provide you precise answer.
#4 kakil
kakil
Posted 12 October 2016 - 04:58 AM
Dear Gents ,
thanks to your reply .
yes it contain expansion tank with 4barg with same elevation with the suction pipe .