Fire - Two Phase Relief From Atm Storage Tank
#1 J_Leo
J_Leo
  • 262 posts
Posted 03 September 2017 - 01:10 PM
Has anybody ever considered two phase fire relief from large atmospheric storage tank? On a project, it is assumed 90% liquid full in storage tanks for fire case.
From an internal document I have, it says if the tank is padded on the bottom and its diameter is greater than 15 ft, then when the liquid (not bubbly-foamy type) level is less than 95%, then two phase relief can be ignored.
Personally, I don't have experience with two phase relief from an atmospheric storage tank. Anybody can give some advice on this?
Thank you.
Leo
#2 AlertO
AlertO
  • 194 posts
Posted 05 September 2017 - 01:38 AM
Hi Leo
Two-phase relief is hardly presented in atm storage tank because only vapor can flow to the top of the tank. This is similar when you boils water in a pot.
#3 fallah
  • 5,019 posts
Posted 05 September 2017 - 02:39 AM
Leo,
Because there is no situation based on which an atmospheric storage tank could be liquid filled especially in fire case; then two phase relief isn't applicable to such tanks...
#4 Pan Nata
Pan Nata
  • 34 posts
Posted 14 September 2017 - 03:42 AM
Leo,
When fire happens thing that over-pressurized your storage tank is vaporized liquid inside the tank hence two phase relief for fire case give no sense for liquid storage tank
#5 latexman
  • 1,819 posts
Posted 14 September 2017 - 08:16 AM
If the company document applies to your specific tank project, I'd follow it and move on to a real problem.
#6 J_Leo
J_Leo
  • 262 posts
Posted 17 September 2017 - 01:43 PM
Dear all,
Thank you so much for your responses. I also read a practice from one EPC company, which says if the liquid level is below 95%, then no two phase relief is required.
-Leo