Lng Vaporizer Isolation Valve Installation
#1 Jay Kim
Jay Kim
  • 3 posts
Posted 10 April 2018 - 06:34 PM
Hello, I have a question with respect to the isolation valve installation standard for LNG Vaporizer.
As per NFPA 59A 2013 edition, where the heated vaporizer is located less than 50 ft from the heat source, it shall have an automatic shutoff valve in the LNG liquid line located at least 10 ft from the vaporizer.
Would you tell me why an automatic shutoff valve shall be located at least 10 ft from the vaporizer?
Thank you.
#2 Bobby Strain
Posted 10 April 2018 - 09:55 PM
Because the NFPA committee thinks it's a good idea. They probably took a vote to establish the distance.
#3 Jay Kim
Jay Kim
  • 3 posts
Posted 11 April 2018 - 08:06 PM
Thanks for your reply, Bobby.
If the isolation valve location shall be considered in accordance with NFPA, can I install it 50 ft from the vaporizer?
What's the reason automatic isolation valve should not be located within 10 ft from the vaporizer?
Thank you.
#4 Pilesar
  • 1,694 posts
Posted 12 April 2018 - 07:56 AM   Best Answer
In case of a fire, you want to have an isolation valve to shut off the fuel source.  The valve controls should not be burned up in the fire which would make it useless.  So put the valve outside the most likely fire danger area.
#5 Jay Kim
Jay Kim
  • 3 posts
Posted 12 April 2018 - 08:28 PM
Thank you, Pilesar. Now I understand.
#6 fallah
  • 5,026 posts
Posted 14 April 2018 - 01:45 AM
Jay Kim,
It's obvious the automatic SDV should be located outside the fire zone to be closed remotely to prevent feeding fire by LNG in fire case; of course if it has to be located inside fire zone it shall be fireproofed one not to be damaged when is engulfed in a pool fire...