Heat Exchanger
heat duty temperature sizing heat exchanger u-tube
#1 navneet2109
navneet2109
  • 35 posts
Posted 13 November 2018 - 12:36 AM
Dear all Engineers,
Please refer attached file while reading this.
as per "DESIGN-1" the sizing of shell & tube heat exchanger has been done. In this design the output of propylene temperature is 40c.
now the client need the propylene at 45c with the same sized heat exchanger.
So as per "DESIGN-2" we can achieve this by changing the input temp of glycol from 50 to 60 C.
In "DESIGN-2" we changed the glycol solution input so the temerature difference become 20C in exchanger 1 (DESIGN-2).
Previously it was 10C (DESIGN-1).
By consulting others regarding this sizing they are not considering 20c difference in exchanger1. so according to consultant we have to change the STHE sizing.
My question here are following:
1. Is there any problem to have 20c difference of glycol solution in exchager1 (40C input and 60 output)?
2. Is there any criteria for considering temperature difference for STHE?
3. Because of this difference the heat duty is increased but the size remains same. So is there anything affecting if the heat duty increased on same sized heat exchanger?
Hope you all understand my concern regarding HE sizing. Any other advice relating to Heat Exchanger you are most welcome.
Attached File  Untitled.png   37.72KB   1 downloads
#2 Bobby Strain
Posted 13 November 2018 - 07:37 PM
You should rate the exchanger with a proper software.
#3 navneet2109
navneet2109
  • 35 posts
Posted 13 November 2018 - 11:25 PM
The screenshot i have attached is from HTRI and from both option i am getting the acceptable design. I think this is the best software for heat exchanger.
Please go through my question again. what i am asking is basically a doubt which i can get from experience personal only.
#4 Pilesar
  • 1,685 posts
Posted 14 November 2018 - 03:24 PM
Experience is something you do not get until just after you need it. You should rate the exchanger with a proper software. Did you use the appropriate inputs? Did you interpret the results correctly? We have no way of knowing.
  It is nice when you can get someone to check your work, but when that is not feasible, you just have to make sure you can defend your conclusion, then call the shot and take the consequences. It is certainly possible that the exchanger is good for the new conditions. If I were reviewing your work, the following checks come to mind:
- Is there any phase change for the fluid?
- Is the heat exchange in the film boiling region?
- Are the velocities acceptable?
- Will the pressure drop work in the hydraulic system?
- Is tube vibration a problem?
- Is the differential thermal expansion accounted for in a fixed tubesheet design?
- Is the pressure relief properly designed?
#5 navneet2109
navneet2109
  • 35 posts
Posted 15 November 2018 - 03:20 AM
I know that i will not get experience when i need it but can't i ask the experience personal if i have any doubt?. I have already mention i used HTRI software.
Yes i used all the inputs correctly for the "DESIGN-1" (attached screenshot). I am getting the result from both way (DESGN-1 AND DESIGN-2). I can't attached the whole calculation. It will be illegal i think.
please the attached. from that it can be find out that phase change is taking place or not.
no boiling
yes velocity is acceptable
for the "DESIGN-2" tube side pressure drop allowed is 0.7kg.cm2 and i am getting 0.68kg/cm2. Is it acceptable or not.
​i am using impingement plate.
its u-tube. for tubesheet we have considered for the expansion.
not required for heat exchanger vessel.
Edited by navneet2109, 15 November 2018 - 03:22 AM.
#6 Chemitofreak
Chemitofreak
  • 292 posts
Posted 16 November 2018 - 09:29 AM
Here are my two cents:
1) There are various glycols available, we don't know which one you are using. Maybe you should search some literature with respect to the glycol you are using, this will help you to check whether the glycol is o.k at 60 degC or it can undergo thermal degradation.
2) Temperature difference across the Heat Ex is solely governed by the process.
3) The Client wants you to increase the outlet temperature of one fluid, by keeping the area constant. That can be done by one of the way you have already tried.
#7 navneet2109
navneet2109
  • 35 posts
Posted 16 November 2018 - 10:56 AM
Your two cents are more valuable.
​I will definitely check glycol properties for 60degC.
You are correct.
By this sentence I have gain little bit confidence that it can be done. My main concern was only that we can go of 20 degC difference.
I am very grateful to you for answering after understanding the points.
regards
Edited by navneet2109, 16 November 2018 - 10:58 AM.