I have a condenser for a platformer stabilizer using cooling water on the tube side. The condensers are near grade and are in a fire zone. The shell side normally operates at about 160 psig. I would expect most of the shell side volume to be vapor and minimal liquid as the condensers free drain.
I am suggesting that the tube side has a fire case and that we should use the surface area of the entire vessel for the heat flux. Along with the exchanger end, it seems that the vapor on the shell side would easily transfer heat from the fire to the tubes with convective currents as the shell temp will rise quickly (no latent heat to temper it).
Is this approach too conservative. My client want to only use the area of the exchanger ends. The difference in PSV sizing is "D" with only ends and "F" using 100% surface area.
i now there is discussion in previous thread of liquids on the shell side heating the tube side in a fire, but the vapor in the shell heating the liquid in the tubes is not a discussion thread i have found yet.
Thank you ahead of time for any assistance in this matter.
Deb S