Hydrogen Vent Sizing And Purging Rate
Posted 19 March 2021 - 03:44 PM
I have to come with a high level estimate of nitrogen demand for continuous purging of hydrogen vents which are open to atmosphere. I have a couple of questions:
1. I know the venting rate and have to calculate the line size of the vent pipes. Is there any typical velocity criteria for sizing the vent tail pipes d/s of the pressure controlled spill-off control valves? For PSV tail pipes joining into a flare header I have come across 0.5 Mach No. but is there any limiting velocity criteria for open vents in hydrogen service?
2. What should be the basis for nitrogen purging rate? Is there a sweeping velocity criteria?
Posted 19 March 2021 - 06:42 PM
The purpose of nitrogen purging is make sure oxygen does not enter the vent system. Five volume turnovers per minute is reasonable for this purpose. Vent velocities should be constrained so that the piping can be supported and vibration does not become a problem. Design vent velocities should be based on your vent rate, pipe size and wall thickness.
See if you can find a copy of NFPA 68 'Standard on Explosion Protection by Deflagration Venting' for reference.
Links to other possibly useful documents:
https://ntrs.nasa.go...ons/19750066661
https://ntrs.nasa.go...19670000098.pdf
https://www.scienced...36031999390067K
Posted 22 March 2021 - 01:56 PM
Posted 22 March 2021 - 04:49 PM
A few documents to support .
Good luck.
Surface Area Calculation For Blowdown Orifice Sizing Including FinnedStarted by Guest_victortheone_* , 17 Feb 2026 |
Drain And Vent Destination LpgStarted by Guest_Priolo_* , 14 Feb 2026 |
Steam Drum SizingStarted by Guest_nastaran_* , 01 Dec 2025 |
Calculating Gas Flow Rate Without CvStarted by Guest_worrier_* , 25 Nov 2025 |
Heat Of Dilution Of Hydrogen Chloride In Hydrochloric Acid Solution (3Started by Guest_fredlan54_* , 21 Nov 2025 |