Inbreathing And Outbreathing Vs. H2S Blanketing Gas System
sweep gas blanket gas inbreathing outbreathing sulphur
10 replies to this topic
#1 gusto88
gusto88
  • 6 posts
Posted 18 October 2021 - 09:13 PM
Hi All,
I am in the process of learning about tank design, specifically a Sulphur tank design according to API 650 with API 2000 venting.
For this design, we need a system to keep H2S levels below explosive limits. I understand these calculations.
However, where I get stuck is:
a) Why would you choose a blanket gas system over a "sweep gas" system for a sulphur tank design?
b ) is a blanket gas OR a sweep gas system completely separate from the in-breathing/out-breathing calculations for the tank design? If they are two separate calculations, are they two separate systems built into the tank?
c) Do I complete the in-breathing/out-breathing calculations and then design a separate system for the sweep gas system? Is there a good textbook or reference for designing these sweep gas systems?
Thanks for any guidance or clarifications.
Edited by gusto88, 18 October 2021 - 09:16 PM.
  • 6,926 posts
Posted 18 October 2021 - 09:44 PM
Consider these 4 documents to support your work ,
H2S is not only flammable , it could lead to fatality .
Good luck,
#3 gusto88
gusto88
  • 6 posts
Posted 19 October 2021 - 02:35 PM
Thanks Breizh,
I looked through the documents you sent. I understand the issue with H2S, and I want to make sure I am doing the calculations correctly.
Still not clear on this item:
Good luck,
#4 gusto88
gusto88
  • 6 posts
Posted 19 October 2021 - 02:36 PM
Are the inbreathing / outbreathing vents completely separate from the "sweeping gas", I think it is, but I want to make sure.
#5 breizh
  • 6,926 posts
Posted 19 October 2021 - 06:41 PM
Yes they are separated , inbreathing/outbreathing through a PVRV and sweeping through N2 regulator .
On the document underneath you will find the set up mentioned above .
#6 gusto88
gusto88
  • 6 posts
Posted 20 October 2021 - 10:31 AM
Hi Breizh,
Does this article apply to Sulphur tank H2S sweeping as well?
#7 gusto88
gusto88
  • 6 posts
Posted 20 October 2021 - 01:39 PM
If we designed a gas sweeping system for a sulphur tank, with a rate of X m3/hour of "sweep gas". Would that X rate of gas be added to the in-breathing and out-breathing? If not, where would these values be added in terms of the tank design?
See our inbreathing and outbreathing values:
Min. out-breathing venting flow rate;        2833 m3/hour     + X m3/hour (sweep gas)?
Min. in-breathing   venting flow rate;         2243 m3/hour    + X m3/hour (sweep gas)?
Emergency venting flow rate;        87492 m3/hour
#8 breizh
  • 6,926 posts
Posted 20 October 2021 - 07:03 PM
I would suggest to consult someone in your organization knowledgeable about Safety, Standard and Code applicable in your area  and/or to hire a contractor to support you .
To me your requirement  is not clear . You need to prepare a PFD /PID together with a process description and the objectives of the project and submit it for review .
note :
I'm adding documents issued by art Montemayor to support you and others .
https://www.oilandga...ten-sulfur-0001
#9 ASalman
ASalman
  • 3 posts
Posted 22 October 2021 - 06:38 AM
Hi Gusto
I suggest reading this article, you may find it useful.
A Salman
#10 gusto88
gusto88
  • 6 posts
Posted 24 October 2021 - 06:02 PM
Thanks for the info guys.
If anyone is very familiar with these designs, can you explain if the in-breathing and out-breathing rates are affected by the gas flow rates of the sweep gas system? (See above). I read through the provided info but I did not find anything that explicitly answers this.
I am sure someone who is very familiar with these designs, can answer this please?
#11 ASalman
ASalman
  • 3 posts
Posted 28 October 2021 - 07:31 AM
Hi Gus
The inbreathing/outbreathing rates will be affected by what goes in and out of your system e.g. transfers or changes in ambient conditions etc.... I would suggest reading the latest version of API 2000 (or whichever standard your organisation follows) it will state the requirements of inbreathing/outbreathing. Tip - a mass balance of the various scenarios will be essential to your solution.