Psa Tail Gas Conditions
psa
7 replies to this topic
#1 daraj
daraj
  • 222 posts
Posted 19 November 2021 - 05:40 AM
for a 12-bed PSA making high purity ydrogen, what is te typical tail gas pressure and temperature? I dont find temperature mentioned anywhere. I believe the product hydrogen comes out at 0.5 bar or less tan feed pressure and at temp close to 50C(correct if wrong)
#2 PingPong
PingPong
  • 1,474 posts
Posted 20 November 2021 - 02:51 PM
For design purposes:
Typical tail gas temperature is about 10 oC lower than PSA feed gas and tail gas pressure downstream buffer vessel and filter is typically 0.35 barg (5 psig). That is to have about 0.3 barg pressure at burner.
Typical hydrogen product temperature is about the same as PSA feed gas, and hydrogen product pressure ex PSA is typically 0.6 bar lower than PSA feed gas.
Note however that there normally is a pressure control valve between PSA and battery limit (BL), so PSA inlet pressure is typically 1 bar higher than the hydrogen BL pressure.
#3 daraj
daraj
  • 222 posts
Posted 21 November 2021 - 05:21 PM
Thanks Pingpong
#4 daraj
daraj
  • 222 posts
Posted 30 December 2021 - 01:34 AM
Pingpong, wanted to confirm this again. considering hot n2 is usually used for bed regen, any reason as to why PSA tail gas should be 10c lower than feed gas? suppose if my feed gas is coming in at 30C say, then tail gas will leave at 20c? (whic is lower than cooling water utility)?
#5 PingPong
PingPong
  • 1,474 posts
Posted 30 December 2021 - 03:42 AM
There is no hot N2 during normal operation.
The tailgas is lowered in pressure and will experience JT cooling.
The licensor designs that I have seen through the years indicate a roughly 10 oC lower temperature in the heat and mass balance, so that's what I mentioned before.
#6 daraj
daraj
  • 222 posts
Posted 01 January 2022 - 05:21 AM
ok,is a presure of 0.3-0.5barg(or 1.3-1.5 bara) reasonable for tail gas?
#7 PingPong
PingPong
  • 1,474 posts
Posted 01 January 2022 - 09:32 AM
As I already wrote before: tail gas pressure downstream buffer vessel and filter is typically 0.35 barg (5 psig). That is to have about 0.3 barg pressure at burner.
#8 gegio1960
gegio1960
  • 518 posts
Posted 02 January 2022 - 04:52 AM
there are situations where a higher h2 recovery is a must.
in these cases a rotary compressor is installed downstream of the tail gas mixing drum in order to minimize the tail gas pressure.
you can go down to 0.1 bara increasing the h2 recovery by several points.
in other words the tail gas pressure is defined by the downstream system pressure.
Edited by gegio1960, 02 January 2022 - 04:56 AM.