Psv Bypass Line Size

psv bypass psv

9 replies to this topic
Share this topic:
| More

#1 R_Gowtham

R_Gowtham

    Junior Member

  • Members
  • 15 posts

Posted 06 June 2022 - 02:17 AM

Hi all,

 

Is any code or standard or good engineering practice available to calculate PSV bypass line size? 

 



#2 breizh

breizh

    Gold Member

  • Admin
  • 6,334 posts

Posted 06 June 2022 - 03:00 AM

Hi ,

Please clarify , you can't  have bypass line on PSV . 

Thanks to describe your scenario.

Breizh



#3 R_Gowtham

R_Gowtham

    Junior Member

  • Members
  • 15 posts

Posted 08 June 2022 - 02:05 AM

Please refer the below image. how to size the yellow highlighted line? 

 

is there any criteria?

Attached Files


Edited by R_Gowtham, 08 June 2022 - 02:06 AM.


#4 breizh

breizh

    Gold Member

  • Admin
  • 6,334 posts

Posted 08 June 2022 - 02:50 AM

Hi,

Consider to read : https://www.cheresou...s-line-for-psv/

 

I don't  see the need for this line .

 

Breizh



#5 Bobby Strain

Bobby Strain

    Gold Member

  • Members
  • 3,529 posts

Posted 08 June 2022 - 10:21 PM

It doesn't appear to be a PSV bypass. But a manual depressuring means, not meant to function as an alternate relief method. Most jurisdictions in the USA allow isolation valves with a single PSV. But a means of manned depressuring mechanism is required. Hence a "bypass" valve.

 

It seems your highlighted line is already sized.

 

Bobby



#6 Chemitofreak

Chemitofreak

    Gold Member

  • Members
  • 291 posts

Posted 10 June 2022 - 03:00 AM

It is a manual depressurizing line. Minimum size used is 2" (same is specified in your P&ID). It can be based on the volume that needs to be depressurized. You should check your philosophy documents for guidance.  



#7 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 10 June 2022 - 11:15 PM

Hi all,

 

Is any code or standard or good engineering practice available to calculate PSV bypass line size? 

 

Hi,

 

Although looks like it's a bypass, the purpose of the mentioned line which is mostly 2" size, isn't really as a PSV bypass. In fact, it is a connection from the vessel to the flare network for maintenance to allow purging when the vessel is out of service.



#8 abhi_agrawa

abhi_agrawa

    Gold Member

  • ChE Plus Subscriber
  • 216 posts

Posted 22 June 2022 - 11:15 AM   Best Answer

This is not a bypass. PSV bypass is a misnomer in itself.

 

Personally, I call this depressuring line. I have used this line extensively during initial start-up. The usual scenario is:

a. You have a vessel filled with Nitrogen and you would like to introduce hydrocarbons in to this vessel.

b. When you introduce Hydrocarbons - where does this Nitrogen go? You cannot open the vent and vent to atmosphere as you may vent hydrocarbons as well, this is dangerous.

c. You need a connection to flare that can be opened to let this Nitrogen go to flare.

 

The line to be used is this so called PSV bypass.

 

The line size should be determined based on how fast you would like to bring in hydrocarbons. For large vessels 2" may not be adequate.

 

Hope this helps,

Abhishek



#9 HMD.Dianat

HMD.Dianat

    Brand New Member

  • Members
  • 2 posts

Posted 25 December 2022 - 11:22 PM

the question is:

if its not PSV bypass and has other applications then "all other vessles which are not equipped with PSV need the same discharge line to flare as well" and this is not true.



#10 fallah

fallah

    Gold Member

  • ChE Plus Subscriber
  • 4,951 posts

Posted 31 December 2022 - 07:12 PM

the question is:

if its not PSV bypass and has other applications then "all other vessles which are not equipped with PSV need the same discharge line to flare as well" and this is not true.

Hi,

 

If the vessels are Pressure Vessels, they are mostly equipped with PSV hence the by pass line for connection to flare; if for any reason they might not be equipped with PSV the connection to flare can be exist without titling it as by pass.