Python Control Library Step_Info Returning Nan For All Parameters
python control modelling
#1 HWIK
HWIK
  • 8 posts
Posted 08 October 2022 - 09:20 AM
Hi, I am running the following code for a unit step response in a closed loop transfer function on Python using the control library in python:
import control as c
kc = 0.9*3/23
d = c.pade(0.3)
Gp = c.tf([1],[1,1])*c.tf(d[0],d[1])
ti = 1
Gc = kc*c.tf([ti, 1], [ti, 0])
sys1 = Gc*Gp/(1+Gc*Gp)
data1 = c.step_info(sys1)
print(data1)
And the output I get:
{'RiseTime': nan, 'SettlingTime': nan, 'SettlingMin': nan, 'SettlingMax': nan, 'Overshoot': nan, 'Undershoot': nan, 'Peak': inf, 'PeakTime': inf, 'SteadyStateValue': nan}
Which isn't correct, as from plotting the step response the output profile is stable, and it parameters such as RiseTime and SettlingTime should be defined. I tried doing it in Matlab and I got specific answers for it. So why is this nan in Python?
Thanks for your time!
#2 Saml
Saml
  • 301 posts
Posted 08 October 2022 - 09:51 AM
May be this?
https://python-contr...ml#installation
Quote
Many parts of python-control will work without slycot, but some functionality is limited or absent, and installation of slycot is recommended. Users can check to insure that slycot is installed correctly by running the command
python -c "import slycot"
#3 HWIK
HWIK
  • 8 posts
Posted 08 October 2022 - 10:09 AM
Saml, on 08 Oct 2022 - 3:01 PM, said:
May be this?
Quote
Thanks for the suggestion! Unfortunately I tried doing that, but it didn't work.
#4 Saml
Saml
  • 301 posts
Posted 09 October 2022 - 07:07 PM
I suppose that in the following line you wanted to write the transfer function of a PI controller. I see many things here:
The parameters in the tf function are a polynomial in s, starting from the higher exponent.
For a PI controller, that function is (in your nomenclature where kc is the proportional constant)
Kc + Ki/s  where Ki is Kc/ti. Taking Kc outside of the equation, then your transfer function is
Kc * (1+s/ti)/s
So the parameters of the Gc transfer function should be:
[1,1/t] and [1,0]
When you write that line as
Gc = kc*c.tf([1,1/ti], [0, 1])
It yields
{'RiseTime': 0.2562817118891321, 'SettlingTime': 0.562166335756806, 'SettlingMin': 0.09475317415593856, 'SettlingMax': 0.10505836575875488, 'Overshoot': 0, 'Undershoot': 126.60098522167488, 'Peak': 0.1330049261083744, 'PeakTime': 0.0, 'SteadyStateValue': 0.10505836575875488}
Now, you would get better answers if you put comments on your code and clarify what the variables mean and what you are intending to do.
I am just guessing that by Kc you wanted to writh the proportional constant but don't have a clue of what 0.9*3/23 means. Why are you using a delay, what "ti" is (may mean temperature or time, initial or integral).
And... by the way. if Gp is the process and Gc is the controller, you have the the transfer function for the closed loop wrong. It is a guess, you don't mention what you are trying to model
Instead of
Gc*Gp/(1+Gc*Gp)
The correct one , if Gc is the transfer function of a PI controller is:
Gp/(1+Gc*Gp)
If that is the case, the results are
{'RiseTime': 2.220933139341779, 'SettlingTime': 4.18058002699629, 'SettlingMin': 0.8064923681896231, 'SettlingMax': 0.8949416342412453, 'Overshoot': 0, 'Undershoot': 4.959759304365055, 'Peak': 0.8937741215508875, 'PeakTime': 6.907755278982151, 'SteadyStateValue': 0.8949416342412453}
Edited by Saml, 09 October 2022 - 07:09 PM.
#5 HWIK
HWIK
  • 8 posts
Posted 10 October 2022 - 06:30 AM
Kc * (1+s/ti)/s
[1,1/t] and [1,0]
It yields
Instead of
Gc*Gp/(1+Gc*Gp)
Gp/(1+Gc*Gp)
Thanks for the reply Saml, I now do realize that the problem may be quite abstract given that I did not include much of an explanation on what is being done there. But your interpretation of the variables and how they are set up is indeed correct.
We were given this problem as part of a process control class, where we were just given the process transfer function (Gp) and we are asked to design a feedback PI controller according to a given set of rules, which to me yielded the values given in kc (proportional gain) and ti (integral time delay) given in the code.
Unfortunately I don't see how you arrive to your controller transfer function:
Which would give: kc*(s+1/ti)/1, which is not in accordance with an ideal PI controller transfer function.
Furthermore, for a feedback loop setup I believe the transfer function I give is correct, where do you lose the Gc term in the numerator?
So I still don't see where the problem would be in the code given in the question.
#6 Saml
Saml
  • 301 posts
Posted 18 October 2022 - 07:54 AM
It is not what you believe. It is the problem you are trying to solve. That you don't tell.
The scheme you show is not how a PI feedback controller works.