Regarding Lube oil pump discharge back pressure control (PCV) for centrifugal compressor driven by steam turbine where is the correct sensing of pressure before Lube oil cooler and filter or after ?
|
|
Lube Oil Pump Back Pressure Control
Started by Divid Kelin, Dec 07 2022 01:55 PM
1 reply to this topic
Share this topic:
#1
Posted 07 December 2022 - 01:55 PM
#2
Posted 07 December 2022 - 08:46 PM
Hi,
You should have sensors to monitor the DP of the filter/oil cooler and a PI before or after to monitor the entire line. DCS or PLC should perform the calculation and generate alarms or thresholds to stop the compressor.
My view