Condensate Relief To Atmosphere
#1 Chemitofreak
Chemitofreak
  • 292 posts
Posted 28 April 2023 - 11:42 AM
I am currently working on relief system for an existing Condensate Recovery system.
MP Condensate is flashed, LP steam is recovered and the condensate is sent to the condensate recovery system
During blocked liquid outlet for the condensate flash drum, there will be liquid overfill and since the operating pressure of the MP steam is higher than the design pressure of the flash drum, it will lead to over pressurization.
The RV is adequately sized, but there will be relief to the atmosphere. The relief will be two phase, but at the moment the relief is to atmosphere like we have for vapour relief. There would be hot water sprayed from the outlet piping of the RV in the current set-up.
The issue is that, based on my past experience, I have never seen RV on a condensate flash drum where-in hot liquid condensate relief is routed to safe location most of them are similar to vapour relief. I assume that in all the condensate system there would be liquid overfill scenario.
Am I missing something, or my view is correct.
Revert in case of any query.
Edited by Chemitofreak, 28 April 2023 - 11:44 AM.
  • 1,639 posts
Posted 28 April 2023 - 12:27 PM
A sketch might help. If I understand the scenario, the condensate recovery system drum normally operates near atmospheric pressure and the maximum inlet pressure will be LP steam pressure from the upstream flash drum. The question is 'what is the safe location for the relief discharge?' Consider relieving to a vertical pipe open at top and bottom. Discharged steam will travel skywards while discharged hot water will travel downwards to grade.
Edited by Pilesar, 28 April 2023 - 12:28 PM.
#3 seuenergy
seuenergy
  • 40 posts
Posted 30 April 2023 - 05:18 AM
what is the design pressure of flash drum?
if the outlet of drum is blocked. and the drum is connected to upstream high pressure process, the drum would be pressurized by MP steam. So the a PSV is needed.
#4 breizh
  • 6,942 posts
Posted 30 April 2023 - 06:12 AM
Yes, the PSV is needed for the reason explained above. To me the problem is where to route the release to prevent people to receive a shower of hot water during release. A Catch pot might be considered.
My view
#5 shvet1
shvet1
  • 476 posts
Posted 01 May 2023 - 11:36 PM   Best Answer
No, this is not a common case.
2-phase relief require some means to separate steam from boiling water and drain/disperse those in a safely manner. I have encountered only 1 such case: a deep underground pit + fence + approach road. Pit has no an outlet and after cooling is emptied by a truck. Good practice is to fill such pit with gravel which helps to avoid shock heating of pit wall. Note that concrete is not suitable for hot water so ceramic or metal is recommended (depends on how often such relief will occur).
More problems in case of a cold region.
This option seems much more expensive than overfill prevention.
Edited by shvet1, 01 May 2023 - 11:39 PM.
#6 Chemitofreak
Chemitofreak
  • 292 posts
Posted 08 May 2023 - 05:25 AM
Thanks a lot for your response guys. Highly appreciated.
Like shvet1 explained, we are also looking at something similar, but it is turning out to be damn expensive.