Hi,
I have this system:
Natural gas from pipeline Oper @ 6200 kPag (with PAHH @ 6700 kPag protection) with a control valve letdown to 5000 kPag. The 5000 kPag side has a PSV set @ 6206 kPag.
My question is - is there a control valve wide open scenario here?
To consider CV wide open,
P(in) = 6700 kPag
P(out) = 6806 kPag (6206 @ 1.1 as per API 521)
==> CV wide open case is not applicable.
Or should I consider P(out) as 6206 kPag to "force" a CV wide open case just to be conservative?
Thank you!
Yincal