Burners Flame Monitoring System Requirement
flame monitoring furnace
#1 Movers
Movers
  • 71 posts
Posted 23 November 2023 - 06:28 AM
I have a question related to requirement of installing flame monitoring system in the furnaces.
If TDL analyser of methane content in flue gas is provided at the furnace bridgewall, can it be treated as enough protection (of course next to  control of firing by field Operators) against extensive methane concentration in the combustion chamber during furnace start up (caused e.g. by lack of the flame)?  And would it be used instead of flame monitoring system?
  • 1,635 posts
Posted 23 November 2023 - 07:06 AM
With such a scheme, the furnace would be at higher risk of rapid unscheduled disassembly.
#3 breizh
  • 6,937 posts
Posted 23 November 2023 - 07:19 AM
Check the regulation in your country and consult the fire brigade.
To me the answer is No!
#4 shvet1
shvet1
  • 476 posts
Posted 24 November 2023 - 12:00 AM
can TDL analyser of methane content in flue gas be treated as enough protection against extensive methane concentration in the combustion chamber during furnace start up
Depends on heater design. See EN 746 for details.
Negative as flame failure is the only allowed controllable parameter of >70kW burners as per standard above.
Edited by shvet1, 24 November 2023 - 12:28 AM.
#5 Movers
Movers
  • 71 posts
Posted 24 November 2023 - 01:48 AM
EN 746-2 describe requirements for the use of flame detectors and it  allows inspection of the furnace during start up to 750°C only by the Operator if he is able to take immediate corrective action if there are any problems with the flame. In our case Operator is able to do it, so in my opinion flame detectors are not needed. But we have discussion if TDL methane analyser can be treated as equivalent protection during start up.
#6 Movers
Movers
  • 71 posts
Posted 24 November 2023 - 03:43 AM
Why do you think that? Can you provide more details?
#7 shvet1
shvet1
  • 476 posts
Posted 26 November 2023 - 11:45 PM
I did not catch the point.
You have asked if ex-components are allowed to be used instead of flame detection during purging procedure. Answer is - no, as EN 746-2 allows only flame failure as a controllable parameter.
If this is incorrect please provide a quote to para. EN 746-2 you have been guided by.