1 reply to this topic
Share this topic:
#1
Posted 13 October 2024 - 01:43 PM
This is regarding a water-cooled motor where air is the primary coolant and water acts as the secondary coolant, with a heat exchanger installed within the motor. I would like to understand the rationale behind limiting the water inlet temperature to 38°C and the water outlet temperature to 43°C.
My understanding is that the water inlet temperature is limited to maintain the primary coolant (air) temperature around 40°C, which aligns with the ambient temperature requirements set by the motor manufacturer. However, I'm unclear about the criteria for the water outlet temperature. To me, a higher water outlet temperature would indicate additional heat removal, which seems advantageous. So why is the water outlet temperature limited to a certain level.
Why only a temperature rise of 5°C?
Below is the copy of datasheet:
Details of water cooling system
No. of cooler:1
Water requirement per cooler:490 LPM
Max. permissible temperature:38°C Of cooling water at inlet
Max. permissible temperature:43°C( 5°C rise) Of cooling water at outlet
Maximum permissible pressure At water outlet:6 Bar.
Water pressure drop through the cooler:0.4 kg/ sq.cm
Temp. of cold air coming out & entering the machine for permissible cooling Water temp.:500C
Temp. rise of air passing through machine at full load:30°C
Air pressure drop through cooler:10 mm WC
Temp. rise of water through cooler:5°C
Protection against leakage of water:Water Leakage Detector.
Arrangement to ensure the water flow:Water Flow Indicator
#2
Posted 18 October 2024 - 12:08 AM
higher temperature rise => less water consumption => less velocity in tubes => higher residues precipitation => higher heat transfer resistance => higher risk of overheating at intermittent abnormal conditions or lack of maintenance
38°C inlet temp is just a handy figure as it is equal to 100°F wich has been widely spread in such sorts of calculations => there is a higher chance for a manufacturer to find some similar/equivalent device from a side project and therefore cut cost of design.
Reply to this topic

Similar Topics
Water Hammer Study: Hysys Dynamics Vs PipenetStarted by Guest_powerox29_* , 07 Apr 2025 |
|
![]() |
||
![]() Steam Carrying Liquid From The Sour Water Stripping TowerStarted by Guest_kaidlut_* , 12 Sep 2024 |
|
![]() |
||
Water TreatmentStarted by Guest_not_mikhail_* , 01 Apr 2025 |
|
![]() |
||
![]() Transfer Water By Gravity - Maximum Velocity CriteriaStarted by Guest_56200358_* , 05 Mar 2025 |
|
![]() |
||
![]() Methanol Water Distillation ColumnStarted by Guest_Kakashi-01_* , 27 Jan 2025 |
|
![]() |