Effect Of Continuous Blow Down To Boiler Feed Water
Started by Dyames027, Nov 21 2024 08:36 PM
industrial boiler water
1 reply to this topic
Share this topic:
#1
Posted 21 November 2024 - 08:36 PM
Can anybody help me understand the effect of Continuous blowdown flow to the Conductivity and Phosphate? Our CBD flow is at 3T/H with a steamflow of 250T/H at 42 barg. From our Blowdown water sample our Conductivity is below the limit but the Phosphate is above the limit. What kind adjustment from CBD i will do? Do i need to increase the flow or reduce it? Thank you in advance.
#2
Posted 21 November 2024 - 10:46 PM
Hi,
Make sure your instruments are well and regularly calibrated.
Ask assistance to the company who supplies chemicals for your water and steam boiler treatment.
Ask a third party or your lab to confirm the analysis.
BTW what are the analytical results and specification required?
EDIT : literature about water and steam treatment.
chapter 11 , link underneath -Veolia
https://www.watertec...water-treatment
https://tehnopribor....using condu.pdf
My 2 cents
Breizh