Flowing Temperature- Psv
#1 stu
stu
  • 89 posts
Posted 17 February 2025 - 02:12 AM
Dear all,
In API 520, under relief orifice sizing calculation equation, for "Q" -relieving capacity and "G" -specific gravity , it is specified as " Q at the flowing temperature & G at the flowing temperature". For thermal expansion orifice sizing, please clarify flowing temperature means relieving temperature or liquid normal operating flow temperature in the system.
thanks
stu
#2 latexman
latexman
  • 1,894 posts
Posted 17 February 2025 - 07:04 AM
For thermal expansion orifice sizing, flowing temperature = relieving temperature = ~ liquid normal operating flow temperature in the system.
#3 stu
stu
  • 89 posts
Posted 17 February 2025 - 07:23 AM
Thanks for the response. The liquid normal operating temp.  is 25 deg.C . If the section of pipe is isolated and its temperature rises to 40 deg.C due to external heat source , to avoid over pressure TRV is considered. So here flowing temperature is 40 deg.C & density  of the liquid to be considered at 40 deg.C for calculation isn't?. Please suggest.
thanks,
Stu.
#4 breizh
  • 6,941 posts
Posted 17 February 2025 - 07:25 AM
yes, 40C (operating condition due to external heat source)