2
Atmospheric Tank Vent Sizing
vent sizing cold water spray
#1 kmic
kmic
  • 3 posts
Posted 30 September 2025 - 05:18 AM
 Hi every body,
I’d like your opinion on sizing an air vent for an atmospheric tank that is CIP-cleaned with alkaline at 80 °C, followed by a pre-rinse with water at
14 °C. I tried to calculate it, but the required air-vent size seems very large.
Known data
  • Tank internal diameter: 2 m
  • Height: 3 m
  • Thickness: 2.5 mm
  • Cold spray (rinse) flow rate: 7.2 kg/s
  • Rinse water temperature: 14 °C
I used the Cold-Spray Condensation (Enthalpy) method. I suspect the result is large because the tank is a thin-walled storage tank without stiffeners and the maximum allowable vacuum (MAV) is low. I’m not sure what I’m missing.
Any advice would be appreciated
  • 6,924 posts
Posted 30 September 2025 - 05:59 AM
API 2000 should be your guide.
Why so cold water? tempered water should be better.
#3 kmic
kmic
  • 3 posts
Posted 01 October 2025 - 01:53 AM
Thanks, Breizh, for the notes.
From what I understand, API 2000 covers normal venting (liquid movement + slow thermal), but for CIP cold-spray steam condensation the demand is much higher, so API alone will under-size the vent.
I assumed very cold rinse water as a worst-case CIP scenario, considering the tank is located in the UK.
Any advice on how to calculate the exact Maximum Allowable Vacuum (MAV) for the tank?
#4 breizh
  • 6,924 posts
Posted 01 October 2025 - 02:54 AM
Consider this link
Steam Out - Atmospheric Tank Relief - Tank Blanketing and Venting - Cheresources.com Community