The Basis Of Calculation To 3% Pressure Loss At The Inlet Of Pressure
Posted 14 March 2026 - 01:25 AM
I agree with the API 520 Part II in which rated capacity is selected. So my question is how to persuade others to follow the requirement of API 520 Part II?
Thank you in advance.
Posted 14 March 2026 - 05:18 AM
As I understand the purpose of the 3% rule, it is designed to avoid relief valve rapidly opening and closing such that it destroys itself. The 3% limit was selected by committee as a guideline that was not originally intended as an inviolable rule for every fluid and relief condition. However, due to lawsuits and legal judgments, relief designs usually go to extraordinary lengths to comply with the rule. There may well be other basis for design that would be perfectly safe. The convincing argument for me is "how would I convince a court jury that I followed recommended industry practice?" This consideration guided me in so many engineering choices I have made. Even where my engineering judgment allowed less conservative selections, the financial risk to my company of lawsuit often dictated final design choices.
Posted 14 March 2026 - 08:48 AM
But while conducting the pressure loss calculation which should be applied, the required capacity or rated capacity?
Yes, definitely the PSV rated capacity, because that will be the flow when the PSV is activated.
If you are not in a position of authority over "others", then peer pressure.
Posted 15 March 2026 - 05:07 PM
Posted 15 March 2026 - 09:36 PM
Consider this resource to support your work
Posted 15 March 2026 - 11:31 PM
Posted 16 March 2026 - 05:41 AM
other references
Posted 16 March 2026 - 05:40 PM
If rupture disc is installed at the inlet of pressure safety valve and its resistance factor K is unknown should it consider its effect on pressure loss? Because while sizing safety valve the 0.9 of Kc factor of rupture disc has been considered.
Posted 16 March 2026 - 11:59 PM
Yes, you should, in case the rupture disk is partially open. I've seen value of Kr about 1.2 -1.3
Posted 17 March 2026 - 05:26 AM
It contributes a lot to the pressure loss calculation?
#11
Posted 17 March 2026 - 07:13 AM
A few documents from Fike.
Any vendors of rupture disk should confirm Kr value for RD and PRV in serie.
Note : Contact them to get their feedback.
Posted 18 March 2026 - 07:54 AM
Pressure BuildupStarted by Guest_Yankee_* , 31 Mar 2026 |
Spray Dryer Nozzle Issue – Pressure Increase And Fines IncreaseStarted by Guest_Ella2365_* , 24 Mar 2026 |
Surface Area Calculation For Blowdown Orifice Sizing Including FinnedStarted by Guest_victortheone_* , 17 Feb 2026 |