I have to second gvdlands for part of his response. If you have the fire triangle, then you have a fire scenario and only you can determine this.
I can tell you that you only need to consider a given elevation above a sustainable fire. By this I mean the fuel must be able to pool within a certain distance below or around the vessel. If the vessel is on a grating, then any spills will fall through the grating to the next solid floor below. That is where the elevation is determined from.
What this elevation is depends on a number of sources. However API RP521 recommends 25 feet. In other words, you consider the first 25 feet above the sustainable fire to determine the exposed surface of the vessel engulfed in the fire.
As far as plot area goes, API RP521 suggests (but is not limited to) a plot area of 2,500 to 5,000 square feet.
Dear pleckenr,
Thanks for your very useful reply.What I underestand is,I shall consider the souce of fires for example vessels including flammable liquids for the case of leak and forming pool fire .I shall cosider 25ft above the level of sustaining pool fire,and upto 5000 ft2 of surface around the fire source.If any equipment which has PSV and located in this height(25 ft) and surface(5000 ft2) of fire source shall be considered in case of external fire relief scenario.What about the other fire scenarios,I mean just pool fire shall be considered?or other fire scenarios shall be considered too.For example jet fire,explosion and so on?And what about the overlaps of the fire zones?If one equipment located in two fire zones and zones have overlap with each other the PSV load shall be considered in both? and for the headres sizing the load which is the most among all fire zones is consedered for sizing?
Thanks for yoy advice
Manizheh