The thing is we cant change process conditions so no low pressure steam or condensate as you purposed, and client wanted a PSV in the very last moment. I think just changing design Pressure in Shellside should be enough to avoid the scenario though (to make it higher...)
I am surprise that the statement "...and client wanted a PSV in the very last moment.". Looking the condition, overpressure protection system is required regardless whether client or other requesting.
One way is to increase the shell side design pressure to match the criteria of tube rupture not credible. The heater would be "protected" from overpressure of high pressure steam. But you have to think a little further the extension of this high design pressure on process line as well as upstream and downstream equipments where there is a potential of blocked in. It is complicated.
QUOTE
Regarding the liquid flashing or not, Joe, how could I check that? as I dont know how much condensate I would have at the tube rupture moment.
As you can read from
HERE, the relieving scenario could be very complicated.Quantity of condensate in the shell side would varies. Similarly quantity of condensate in steam relieve through the PRD would varies.
As for PRD sizing, you may consider to use the Leung omega method to estimate quantity of condensate through the orifice (ruptured tube).