Dear colleagues,
I would much appreciate if you could provide me an ‘average value’ for the LPG bulk modulus of elasticity.
I had a look on the Internet but I cannot find this information.
I need this data to estimate the ‘celerity of the pressure waves’
travelling through an LPG section of pipe after a sudden closing of a valve.
Best regards,
Salvatore Spiezia
|

Lpg Bulk Modulus Of Elasticity
Started by salvatorespiezia, Feb 26 2004 11:54 AM
7 replies to this topic
Share this topic:
#1
Posted 26 February 2004 - 11:54 AM
#2
Posted 26 February 2004 - 12:48 PM
As you probably know LPG is basically a mixture of propane and butane.
Bulk modulus of propane is 0.22 GPa (Giga Pascal) at temperature of 20 °C.
Bulk modulus of butane is 0.36 GPa (Giga Pascal) at temperature of 20 °C.
This is relatively low compared to bulk modulus of water (=2.2 GPa), resulting in lower surge pressures.
Bulk modulus of propane is 0.22 GPa (Giga Pascal) at temperature of 20 °C.
Bulk modulus of butane is 0.36 GPa (Giga Pascal) at temperature of 20 °C.
This is relatively low compared to bulk modulus of water (=2.2 GPa), resulting in lower surge pressures.
#3
Posted 04 May 2009 - 03:39 AM
QUOTE (gvdlans @ Feb 26 2004, 11:18 PM) <{POST_SNAPBACK}>
As you probably know LPG is basically a mixture of propane and butane.
Bulk modulus of propane is 0.22 GPa (Giga Pascal) at temperature of 20 °C.
Bulk modulus of butane is 0.36 GPa (Giga Pascal) at temperature of 20 °C.
This is relatively low compared to bulk modulus of water (=2.2 GPa), resulting in lower surge pressures.
Bulk modulus of propane is 0.22 GPa (Giga Pascal) at temperature of 20 °C.
Bulk modulus of butane is 0.36 GPa (Giga Pascal) at temperature of 20 °C.
This is relatively low compared to bulk modulus of water (=2.2 GPa), resulting in lower surge pressures.
gvlands,
Kindly can you please provide a source for this data. or any other reference where the liquid bulk modulus of elasticity could be found?
Also for LPG should we consider an aritmatic average of the above values of use the formula.
sigma xiMi
where xi is the wt fraction of the components
and Mi is the modulus of elasticity of the components making up the LPG
Help appreciated.
Regards
SPOOK
#4
Posted 04 May 2009 - 04:26 AM
QUOTE (SPOOK @ May 4 2009, 10:39 AM) <{POST_SNAPBACK}>
gvlands,
Kindly can you please provide a source for this data. or any other reference where the liquid bulk modulus of elasticity could be found?
Also for LPG should we consider an aritmatic average of the above values of use the formula.
sigma xiMi
where xi is the wt fraction of the components
and Mi is the modulus of elasticity of the components making up the LPG
Help appreciated.
Regards
SPOOK
Kindly can you please provide a source for this data. or any other reference where the liquid bulk modulus of elasticity could be found?
Also for LPG should we consider an aritmatic average of the above values of use the formula.
sigma xiMi
where xi is the wt fraction of the components
and Mi is the modulus of elasticity of the components making up the LPG
Help appreciated.
Regards
SPOOK
Some editions of CRC Handbook of Chemistry and Physics contained tables with liquid compressibility (=1/bulk modulus). I will check my version when I am back home.
I would use a conservative value of 0.36 GPa for LPG, although probably a weighed average ("Sigma xiMi") would be a best estimate.
Anyway, I have done quite a few Pipenet calculations on LPG pipelines (several kilometers in length) in the past and found that surge/waterhammer is hardly any issue with LPG because of the low bulk modulus (= high liquid compressibility).
#5
Posted 04 May 2009 - 04:49 AM
Dear salvatorespiezia&spook,
My observation while with my previous employeris that; on a few Kilometers long LPG pipeline no water hammer like problems throughout the operations spreaded over several years.
Hope this helps.
#6
Posted 04 May 2009 - 05:01 AM
QUOTE (gvdlans @ May 4 2009, 02:56 PM) <{POST_SNAPBACK}>
Some editions of CRC Handbook of Chemistry and Physics contained tables with liquid compressibility (=1/bulk modulus). I will check my version when I am back home.
I would use a conservative value of 0.36 GPa for LPG, although probably a weighed average (xiMi) would be a best estimate.
Anyway, I have done quite a few Pipenet calculations on LPG pipelines (several kilometers in length) in the past and found that surge/waterhammer is hardly any issue with LPG because of the low bulk modulus (= high liquid compressibility).
I would use a conservative value of 0.36 GPa for LPG, although probably a weighed average (xiMi) would be a best estimate.
Anyway, I have done quite a few Pipenet calculations on LPG pipelines (several kilometers in length) in the past and found that surge/waterhammer is hardly any issue with LPG because of the low bulk modulus (= high liquid compressibility).
Thanks gvlands,
your help was indeed insightful.
SPOOK
#7
Posted 04 May 2009 - 05:06 AM
[/quote]
Dear salvatorespiezia&spook,
My observation while with my previous employeris that; on a few Kilometers long LPG pipeline no water hammer like problems throughout the operations spreaded over several years.
Hope this helps.
[/quote]
Qalander,
If the pipelines are designed considering the surge scenarios obviously the water hammer issues will not result. Can you give details about your experience where in emergency situations hammers did not occur.
Appreciated
SPOOK
Dear salvatorespiezia&spook,
My observation while with my previous employeris that; on a few Kilometers long LPG pipeline no water hammer like problems throughout the operations spreaded over several years.
Hope this helps.
[/quote]
Qalander,
If the pipelines are designed considering the surge scenarios obviously the water hammer issues will not result. Can you give details about your experience where in emergency situations hammers did not occur.
Appreciated
SPOOK
#8
Posted 07 May 2009 - 11:40 PM
QUOTE (gvdlans @ May 4 2009, 11:26 AM) <{POST_SNAPBACK}>
Some editions of CRC Handbook of Chemistry and Physics contained tables with liquid compressibility (=1/bulk modulus). I will check my version when I am back home.
The CRC Handbook of Chemistry and Physics does contain a table "Isothermal Compressibility of Liquids" (on pages F-12 - F15 in the 67th edition), but there is no data for propane or butane. The following book does contain a value for bulk compressibility (0.53 GPa at -5 degC) for butane:
SIGTTO guidelines
Similar Topics
Bulk Residence Time In Naphtha CrackingStarted by Guest_mehul_* , 19 Oct 2018 |
|
![]() |
||
Simulating A Liquid Mud Plant And A Dry Bulk PlantStarted by Guest_ebi4exploit_* , 07 Aug 2018 |
|
![]() |
||
![]() Particle Size Vs Bulk DensityStarted by Guest_sateeshkumar830_* , 20 Aug 2015 |
|
![]()
|
||
Bulk Bleach Delivery SystemStarted by Guest_Subject_Name_Here_* , 03 Jun 2016 |
|
![]()
|
||
![]() Recommended Valve Type For 32% Hydrochloric Acid Bulk Storage Main OutStarted by Guest_cravindran_* , 11 Nov 2015 |
|
![]()
|