How does one anticipate the flowrate and blowdown flowrates in a cooling tower?

#2 mbeychok

mbeychok

    Gold Member

  • ChE Plus Subscriber
  • 364 posts

Posted 06 May 2004 - 01:33 PM

Harry:

For a circulating cooling water system with an evaporative cooling tower, here are the pertinent equations:

A water mass balance of the system is:
M = E+D+W

Combining the water balance with a chloride balance of the system:
Cycles = M/(D+W)
Cycles = 1 + E/(D+W)
Cycles = M/(M-E)

where:
Cycles = cycles of concentration
Cycles = (Chlorides concentration in C) / (Chlorides concentration in M)
M = make-up water in volume/minute
E = evaporation in volume/minute
D = draw-off or blowdown in volume/minute
W = windage loss in volume/minute

The evaporation, E. can be obtained by a heat balance:
E = C(dT)(Cp)/H

where:
E = evaporation in gallons/minute
C = circulating water in gallons/min
H = heat of vaporization of water = approx. 1000 Btu/pound
Cp = specific heat of water = 1 Btu/pound/°F
dT = delta T = water temperature drop from top to bottom of tower

The windage loss, W, can be approximated by using:
W = 0.3 to 1.0 percent of C for a natural draft tower
W = 0.1 to 0.3 percent of C for an induced draft tower
W = approx. 0.01 percent of C if tower has windage drift eliminators

To use the above equations, you must first obtain:

(1) The circulating rate of water, C, in volume units/minute.
(2) The concentration of chlorides in the circulating water, C, and in the draw-off, D.
(3) The design windage rate from the tower manufacturer. If that is not possible, refer to the above approximations.

The typical range of cycles of concentration in cooling towers used in petroleum refineries is from 3 to 7. Cooling towers in large power plants will have much higher cycles.

#3 Guest_Ben Thayer_*

Guest_Ben Thayer_*
  • guestGuests

Posted 06 May 2004 - 02:45 PM

WOW! Milton, nice job! A very good and detailed description. Especially including nice rules of thumb for the windage. I am printing a copy to include with my notes.

The cycles you mentioned of from 3 to 7 were also very close to our experiences. The item that affected this was our treatment chemicals and the quality of the makeup water.

Originally we had well water with quite high hardness and ran 3+ cycles. Later we switched to "river" water that was essentially "raw" make-up water to our local city system and increased the cycles to nearly 7.

The increase in our cycles let us significantly reduce our chemical treatment costs.