Hello,
We are installing a 10" PORV where we have to option.
1) build a new 10" nozzle on tank .
2) Tank has a 24" bling on the roof (10" height).Install this PORV on this 24" flange ,with a short 10" nozzle(10" height) on this flange .
The Set pressure for the PORV is 1.5 KPag (0.21 psig).
My question is , if i use option 2), how do i calculate inlet pressure drop using "K" value.I calculated "K" value using equation given on crane paper,page A-26(SI)?I ran a SINET simulation and it gives pressure drop of about 28% of set pressure(largely because 28" to 10" sudden contraction).
thanks all.
|

Porv Installation
Started by cmp74, Oct 12 2008 09:57 AM
2 replies to this topic
Share this topic:
#1
Posted 12 October 2008 - 09:57 AM
#2
Posted 13 October 2008 - 01:04 PM
I would ignore the presence of the 24" or 28" short segment. It has six times the cross-sectional area or roughly 1/36 * the kinetic energy compared to the 10" segment. Essentially all your dP can be considered the tank to 10" segment entrance loss.
#3
Posted 15 October 2008 - 03:45 PM
No surprise with low set pressure of 1.5 kPag. Connect the pilot to the 28" flange. Ensure the PORV is size for CORRECT differential pressure to avoid undersized PORV.
Similar Topics
![]() Recommended Installation Location For "pressure High" InterlocStarted by Guest_omupei_* , 20 Jun 2025 |
|
![]() |
||
Petro-Sim InstallationStarted by Guest_Divid Kelin_* , 27 Apr 2021 |
|
![]() |
||
![]() ![]() Buffer Tank Installation Requirement For Nitrogen Supply.Started by Guest_Younghun Kim_* , 04 Oct 2021 |
|
![]() |
||
Multi-Phase Sensor Installation Guideline (Pressure, Temperature)Started by Guest_Younghun Kim_* , 14 Sep 2021 |
|
![]() |
||
Restricted Orifice Sizing And Installation CriteriaStarted by Guest_CSNK_* , 05 Sep 2017 |
|
![]() |