hello,
I am new to this form.
I want to share a issue and seek expert view on it,
Expansion tank.
I am seeking the help on the above said topic.
I have received a design of water system. In this system we have two loops, close and open loop system.
Interface between the two system is a plate type heat exchanger.
Close loop system is feeding water to the plant at 50 deg C. and returns at 55 deg C.
The return water is fed to centrifugal pump with a head of 78 mtr. , flow 750 cum X 2 pumps running. The return pressure of this water is expected to come back after passing the coolers at 3 ~ 4 bars
In this system we have an expansion tank. This tank is used as a make up of close loop incase of any water loss in the system.
Water is fed to this tank through a pump and pump operation is controlled by the pressure in the supply pipe line of this tank.
There is an automatic FLOAT valve used to shut the supply of water to expansion tank ,on reaching to the required level. Once the tank level is attained, the valve shuts off and the line pressure increase which gives signal to the pressure switch and pump stops.
The discharge from this tank is taken to the suction of close loop system.
This tank is having a overflow line and a vent on the top.
Tank bottom is at a elevation of 6.5 mtr.
How can this tank work as an expansion tank?
Now my thinking, how the system should have been is as under, pl. correct me if I am wrong.
1) What I believe is that this tank should be pressurized and the pressure in side the tank should be more than the pressure of the close loop pump suction pressure. Then only it serve the purpose of making up of water loses.
2) Or the return water from the plant should have been sent in side the expansion tank and the outlet of the tank should have been fed to the close loop pump suction.
If correct me if I am wrong as far as the above two points are concerned pl correct me.
Now the piping is almost complete and the option 2 is ruled out (for my academic knowledge I want to know weather the option two was a better on or not.)
As far point 1, is concerned this can be done with minimum changes in piping.
Now my question is how make use of this system as most of the piping is done as per the attached drawing .
what should have been the best system.
regards