Dear all,
Considering below statement included in API 521 section 5.15.1.1:
"To determine vapour generation, it is necessary to recognize only that portion of the vessel that is wetted by
its internal liquid and is equal to or less than 7,6 m (25 ft) above the source of flame.
NOTE: Hydrocarbon fires can exceed 40 m (approx. 130 ft) in height; however, experience has shown that it is
necessary only to size relief devices on the basis of the averaged heat input up to a height of 7,6 m (25 ft) above the base
of a pool fire."
As you know when bottom of vessel would be below the 7.6 m height from the source of flame,equations 6 to 12 in section 5 of API 521 can be used for relief load determination in fire case.
But if the bottom of vessel would be above the 7.6 m height from the source of flame,
1-For vessel having wetted/unwetted wall,as per above statement,what would be the basics for relief load calculations?
2-What is the height limit for considering fire effect on vessel leading to its cotainment relief?Is that limit such that the level of the vessel bottom would be below than 40 m height from source of flame(as per above API statement)?
Thanks in advance
|

Relief Load Determination In Fire Case As Per Api 521
Started by fallah, Apr 18 2009 01:07 AM
4 replies to this topic
Share this topic:
#1
Posted 18 April 2009 - 01:07 AM
#2
Posted 18 April 2009 - 03:31 AM
If the bottom of the vessel is above the 7.6 m height above the source of the flame, no portion of the vessel is equal to or less than 7.6 m above the source of the flame and therefore relief device does not need to be sized for the fire case.
#3
Posted 18 April 2009 - 04:21 AM
QUOTE (gvdlans @ Apr 18 2009, 04:31 AM) <{POST_SNAPBACK}>
If the bottom of the vessel is above the 7.6 m height above the source of the flame, no portion of the vessel is equal to or less than 7.6 m above the source of the flame and therefore relief device does not need to be sized for the fire case.
Thanks for your prompt reply.
I personally thought same as you in this regard,but i couldn't find any fact in API 521 clearly states your above mentioned point.Would you please submit the fact (if any) included in API 521 you are reffering on for your conclusion?
#4
Posted 18 April 2009 - 05:24 AM
I think the quotes you give in your opening post are pretty clear.
#5
Posted 18 April 2009 - 05:45 AM
QUOTE (gvdlans @ Apr 18 2009, 06:24 AM) <{POST_SNAPBACK}>
I think the quotes you give in your opening post are pretty clear.
Based on what to be discussed,can we say for a vessel that only fire case would be applicable and its bottom is above 7.6 m height from the fire source,there is no need to considering any PSV for its protection?
Similar Topics
![]() Storage Tank Relief LoadStarted by Guest_hum464_* , 10 Sep 2025 |
|
![]() |
||
![]() Is Emergency Venting Required For Polyethylene Storage Tank In Fire ScStarted by Guest_chem55_* , 01 Aug 2025 |
|
![]() |
||
![]() Relief Path To Be Considered For Inlet Pressure Drop CalculationStarted by Guest_Ascanio E._* , 09 Jul 2025 |
|
![]() |
||
Parallel Control Valves Downstream Relief ScenarioStarted by Guest_pklavinsJ_* , 18 Jun 2025 |
|
![]() |
||
![]() Valve Cavity - Pressure Relief ValveStarted by Guest_CS10_* , 20 Feb 2025 |
|
![]() |