why two valves are required at battery limit.
|

Battery Limit
Started by raju333, May 19 2009 09:38 AM
4 replies to this topic
Share this topic:
#1
Posted 19 May 2009 - 09:38 AM
#2
Posted 19 May 2009 - 06:57 PM
This is an example of a typical BL arrangement:

Let me give you this scenario. You've decided to isolate a certain area of a plant. Obviously you need to close all the lines going in and coming out of the area to be isolated.
See the spectacle blind? What's its purpose? How do you engage it from open to close without the valve arrangement?
Hope that answers your question

Let me give you this scenario. You've decided to isolate a certain area of a plant. Obviously you need to close all the lines going in and coming out of the area to be isolated.
See the spectacle blind? What's its purpose? How do you engage it from open to close without the valve arrangement?
Hope that answers your question

#3
Posted 19 May 2009 - 11:35 PM
Other reason (but may not only applicable to BL) could be minimize hazard due to valve leakage.
#4
Posted 19 May 2009 - 11:56 PM
QUOTE (raju333 @ May 19 2009, 10:38 AM) <{POST_SNAPBACK}>
Hi
why two valves are required at battery limit.
why two valves are required at battery limit.
In an emergency you need to isolate your plant from the usually massive inventory in the pipeline beyond. The reliability of closure of a single valve is not really very high therefore 2 valves are often needed to achieve the required Probability of Failure on Demand (PFD) of the isolation function, i.e. to achieve the required Safety Integrity Level (see IEC 61511).
#5
Posted 20 May 2009 - 12:37 AM
QUOTE (JoeWong @ May 20 2009, 01:35 PM) <{POST_SNAPBACK}>
Other reason (but may not only applicable to BL) could be minimize hazard due to valve leakage.
That's another scenario that I'm thinking, although this is not only limited to B/L.
And this is usually employed on high pressures or for mitigating valve leakage (maybe because of fluid toxicity).
Although this is just plain guesswork for us since the OP did not elaborate further on the configuration of the double valve he/she's asking.
Similar Topics
Detection Limit Of Protein SwabsStarted by Guest_Hartwa_* , 12 Feb 2025 |
|
![]() |
||
Electric Heater In Regeneration Absorption BatteryStarted by Guest_alaasleem2026_* , 01 Sep 2024 |
|
![]() |
||
Superheat Limit TemperatureStarted by Guest_phoenixmoca_* , 28 Sep 2022 |
|
![]() |
||
Limit Switch/position SwitchStarted by Guest_panoska_* , 25 Jul 2022 |
|
![]() |
||
Psv Set Pressure Limit In Api 526Started by Guest_SL89_* , 04 Feb 2020 |
|
![]() |