Nfpa 30 Vs. Api 521 Fire Case Heat Input


This topic has been archived. This means that you cannot reply to this topic.
3 replies to this topic
Share this topic:
| More

#1 uiucche94

uiucche94

    Brand New Member

  • Store Customers
  • 4 posts

Posted 15 June 2009 - 10:43 AM

I am in the process of reviewing a set of relief calculations that were done for a project put on hold over a year ago that is now active again. The sizing calcs were done for fire case in a series of different size vessels with all the PSV's discharging in to a common header. When I repeated some of the calculations using API 521 methods, I was coming up with significantly different relief loads. Upon further investigation, I found that the original calculations were done using heat input values calculated based on NFPA 30 (2008 Edition). For values of wetted surface area up 200 square feet, the two methods are pretty close, but once WSA exceeds 200 square feet, they are significantly different - with NFPA 30 giving much higher relief rates (approximately double in some cases). Is the use of NFPA 30 appropriate for the case of ASME pressure vessels in a process area? It gives much more conservative sizing, but it also results in a much larger discharge header and relief devices.

Unfortunately, the original design was done by an engineering firm that employed a process engineer on a contract basis, and he cannot be located - otherwise I would be asking him this question!!

Any help from the pro's would be much appreciated!

Best Regards.

#2 gvdlans

gvdlans

    Gold Member

  • ChE Plus Subscriber
  • 619 posts

Posted 15 June 2009 - 11:16 AM

NFPA 30 is used for low pressure storage tanks, not for pressure vessels. See also http://www.chemcad.c...oads/MNL036.pdf , pages 13 and 14 and Appendix IV. Note that there are more differences between NFPA 30, API 2000 and API 521, for example in how to calculate the wetted area. Personally I would not be worried by using the equations from API Std 521.

#3 demank

demank

    Gold Member

  • ChE Plus Subscriber
  • 150 posts

Posted 15 June 2009 - 08:04 PM

yes of course.
the first step what you must confirmed is the design pressure of tank/vessel.
cause different case of design pressure of tank will take a different calculation.
Btw2, in my opinion, in both case for wetted area calculation must be the same.
for example 25/30 feet above the ground.

#4 skearse

skearse

    Veteran Member

  • Inactive Member
  • PipPipPip
  • 42 posts

Posted 16 June 2009 - 04:35 PM

QUOTE (gvdlans @ Jun 15 2009, 11:16 AM) <{POST_SNAPBACK}>
NFPA 30 is used for low pressure storage tanks, not for process vessels. See also http://www.chemcad.c...oads/MNL036.pdf , pages 13 and 14 and Appendix IV. Note that there are more differences between NFPA 30, API 2000 and API 521, for example in how to calculate the wetted area. Personally I would not be worried by using the equations from API Std 521.


Agreed.