Cooling Water Requirements
Started by Naeema, Aug 12 2009 04:00 AM
Posted 12 August 2009 - 04:00 AM
Hi
I would like to know if there is a formula to calculate the cooling water required for a back pressure turbine. The plant is currently using 3 generators each producing 7MW. they would like to use them to produce the maximum of 12 MW each. I need to calculate the amount of extra cooling water that will be required
Posted 14 August 2011 - 06:38 AM
Hi
Hi Naeema,
Its a quite interesting topic.. First let me clarify ma doubts.. Whether they are using a back pressure turbine? Bcos if it is only a BP Turbine normally they ll be using the letdown steam as a process steam( either MP or LP Steam depending upon the requirement) and there is no requirement for cooling water.. If it is a Condensing type or an Extraction cum condensing type you can worry about the cooling water requirement.. Hope am not wrong..
So here comes the method:
1. Calculate the steam requirement for the power output.
2. Using the steam flowrate calculate the Heat duty. (Q = m*lamda)
3. Then for the required duty calculate the cooling water required. (Q= m*Cp* Dt)
Edited by jpm.chem, 14 August 2011 - 06:50 AM.
Posted 24 August 2011 - 09:35 AM
Rightly mentioned by jpm, Naeema it seems that you first need to understand exactly what type of process you are using in your turbine.
Backpressure - generally means only enthalpy / energy extraction from high pressure steam & outlet is low pressure steam. There is no condensation. Therefore, no cooling water required.
Condensing / Exhaust turbines - means whole steam is condensed at the outlet generally under vacuum. This requires maximum amount of cooling water.
Extraction cum condensing - Its a combination of both systems explained above i.e. some part is coming out as low pressure steam & remaining is condensed.
In all the cases, same principal applies of heat removal for condensation of steam should be equal to the energy gained by cooling water flow rate.
![]() What Kind Of Cooling System Should I Use To Cool Down A Jacketed MixinStarted by Guest_HollyBoni_* , 31 Jan 2025 |