How does one size a line which is connected to a laboratory fume hood at one end and a fan/blower at the other. The fan/blower is discharging to atmosphere.
Flow is 250-300 cfm.
Duct length is around 30 m.
Is there a velocity/pressure drop criteria ?
I have come up with a line size of 6" considering a velocity of 15-20 m/s and
This particular fan/blower can develop a head of 50 mm WC. If it is supposed to discharge to atmosphere, then pressure drop in inlet line should be <= 50 mm WC.
What could cause it to deliver lower than desired capacity ? Is shape of the mouth of the hood important ?
|

Design Of Ducts For Fans
Started by , Aug 12 2009 06:02 AM
1 reply to this topic
Share this topic:
#1
Posted 12 August 2009 - 06:02 AM
#2
Posted 12 August 2009 - 07:13 AM
Among other reasons, lower than 'desired' capacity can be because of
1) higher dP - A discharge velocity of 5m/s will be more appropriate
2) positioning of suction hood - is the fume hood much above where the fume is generated?
3) wet bulb temp - What's the actual density of gas and what's the assumed density?
1) higher dP - A discharge velocity of 5m/s will be more appropriate
2) positioning of suction hood - is the fume hood much above where the fume is generated?
3) wet bulb temp - What's the actual density of gas and what's the assumed density?
Similar Topics
![]() Scrubber DesignStarted by Guest_nasss_* , 07 Aug 2024 |
|
![]() |
||
Refinery Lpg Deethanizer Column DesignStarted by Guest_Ilyes_* , 15 Feb 2025 |
|
![]() |
||
Alkaline Electrolytic Cell/stack Sizing/design For H2 ProductionStarted by Guest_BRS09_* , 13 Mar 2025 |
|
![]() |
||
![]() Heat Exchanger Network DesignStarted by Guest_Kakashi-01_* , 21 Feb 2025 |
|
![]() |
||
Gas-Liquid Separator Design With CondenserStarted by Guest_shambola_* , 16 Jan 2025 |
|
![]() |