Dear Forum Members,
hello,
I have a problem with fans; "combining different static pressure fans in common duct"
I am using fans to maintain bottom temp of a hot bath.
I have two fan runing togather of same model, capacity in a common duct.
The static pressure of these 2 fans is 504 & 494 mm Aq .These fans have been running for last 10 years.
Now my air requirement has gone up. I have a spare fan with static pressure of 388 mm Aq. .
I want to know if I club this spare fan with the two running fans in same duct on which the orginal two fans are running;
will spare fan air get supressed because of less static pressure.
If yes what is the soloution for this if i want to utillise this spare fan to increase the air flow.
|

Static Pressure
Started by vinod kumar turki, Nov 05 2009 09:33 AM
1 reply to this topic
Share this topic:
#1
Posted 05 November 2009 - 09:33 AM
#2
Posted 05 November 2009 - 02:18 PM
Yes
A higher flow through the system will require a discharge pressure over 500. All fan will run back on their curves to generate the higher pressure if they are capable of such a pressure. I would try to speed up the spare fan.
A higher flow through the system will require a discharge pressure over 500. All fan will run back on their curves to generate the higher pressure if they are capable of such a pressure. I would try to speed up the spare fan.
Similar Topics
Hysys Depressuring Utility Pressure QuestionStarted by Guest_cammycheme_* , 15 Aug 2025 |
|
![]() |
||
Static Simulation Of An Atmospheric CduStarted by Guest_tomr91_* , 10 Aug 2025 |
|
![]() |
||
![]() Relief Path To Be Considered For Inlet Pressure Drop CalculationStarted by Guest_Ascanio E._* , 09 Jul 2025 |
|
![]() |
||
![]() Negative Pressure Discharge / Negative At High PointStarted by Guest_felderosfelder101021_* , 05 Jul 2025 |
|
![]() |
||
![]() Rupture Disc Failure Well Below Max PressureStarted by Guest_vaibhav02_* , 02 Jul 2025 |
|
![]() |