I am currently reviewing some PSV calcs for vertical vessels with external fire scenarios.AP 521 (page 36 or 37) says that bottom head area of vertical vessels can be excluded from wetted area ,if vessel is supported by skirt with vent holes.It also says in the designer has to clarify on the area of the connected piping.
Is this a common practice?
thanks in advance
I am currently reviewing some PSV calcs for vertical vessels with external fire scenarios.AP 521 (page 36 or 37) says that bottom head area of vertical vessels can be excluded from wetted area ,if vessel is supported by skirt with vent holes.It also says in the designer has to clarify on the area of the connected piping.
Is this a common practice?
thanks in advance
#2
Posted 05 February 2010 - 04:33 PM
Hello,
I am currently reviewing some PSV calcs for vertical vessels with external fire scenarios.AP 521 (page 36 or 37) says that bottom head area of vertical vessels can be excluded from wetted area ,if vessel is supported by skirt with vent holes.It also says in the designer has to clarify on the area of the connected piping.
Is this a common practice?
thanks in advance
Why not ? Vessel (vertical in particular) with skirt and sitting on concrete slab avoid fire reaching vessel bottom. This minimum fire relief load.
One shall take note that if there may be opening at the skirt for man entry for maintenance, then potential of reach vessel bottom may need to assess.
Piping with liquid possibly expose to fire as well. This will contributes to fire relief also.
Similar Topics
Steam On Shell Side Of A Vertical HexStarted by Guest_Lyne_* , 09 Jul 2025 |
|
![]() |
||
![]() Distillation Column Top & Bottom TemperaturesStarted by Guest_halkeshhulk_* , 09 Jun 2025 |
|
![]() |
||
![]() Distillation Tower Top And Bottom Temperature And PressureStarted by Guest_student55_* , 27 Mar 2016 |
|
![]()
|
||
Batch Adsorption: H/d Ratio For Vessel SizingStarted by Guest_Victor_process_Engineer_* , 28 Feb 2025 |
|
![]() |
||
![]() Storage Tanks Diked Area Fire Protection Using Foam MakerStarted by Guest_mkhattaby_* , 30 Jan 2025 |
|
![]() |