Newest Articles
ChExpress-June 23, 2009
ChExpress-June 9, 2009
ChExpress-May 26, 2009
ChExpress-May 14, 2009
ChExpress-April 28, 2009
ChExpress-April 14, 2009
ChExpress-March 31, 2009
Electrical Process Tomography
Biodiesel: The Road Ahead
Methanol Plant Capacity Enhancement
Plate and Frame Heat Exchangers: Preliminary Design
Compressor Surging Under Control
Using RPM to Manage Maintenance
Plant and Equipment Wellness, Part 1: Observing Variability



banner2.gif (6526 bytes)


Making Decisions with Insulation

rv1.gif (7174 bytes)

This article has been developed into an online Continuing Education (CE) course at RedVector.com. 

Order this CE Course Now

and get a 10% discount by using coupon code "cheresources"

More on Heat Transfer from Cheresources.com:
FREE Resources
Article: Basics of Vaporization
Questions and Answers: Heat Transfer
Experienced-Based Rules for Heat Exchangers and Evaporators
ChE Links: Search for "Heat Transfer"
Students: Ask a Question in our Forums
Professionals: Ask a Question in our Forums
Purchase / Subscription Resources
Book: Available Titles
Online Store: Shell and Tube Exchanger Specification Sheet
Online Store: Heat Transfer Category

Many people overlook the importance of insulation in the chemical industry.  Some estimates have predicted that insulation in U.S. industry alone saves approximately 200 million barrels of oil every year.  While placing
insulation onto a pipe is fairly easy, resolving issues such as what type of insulation to use and how much is not so easy.   Insulation is available in nearly any material imaginable.  The most important characteristics of any insulation material include a low thermal conductivity, low tendency toward absorbing water, and of course the material should be inexpensive.   In the chemical industry, the most common insulators are various types of calcium silicate or fiberglass.  Calcium silicate is generally more appropriate for temperatures above 225 0C (437 0F), while fiberglass is generally used at temperatures below 225 0C.

 Figure 1: Thermal Conductivity of Calcium Silicate Insulation

  Figure 2: Thermal Conductivity of Fiberglass Insulation

A Brief Look at Theory

   The most basic model for insulation on a pipe is shown below.  R1 and R2 show the inside and outside radius of the pipe respectively.  R3 shows the radius of the insulation.  Typically when dealing with insulations, engineers must be concerned with linear heat loss or heat loss per unit length.

inseq1.gif (1730 bytes) align=left             ins1.gif (2566 bytes) align=right
Generally, the heat transfer coefficient of ambient air is 40 W/m2 K.   This coefficient can of course increase with wind velocity if the pipe is outside.   A good estimate for an outdoor air coefficient in warm climates with wind speeds under 15 mph is around 50 W/m2 K.  The total heat loss per unit length can then be calculated by:
inseq2.gif (1381 bytes)             (2)
Since heat loss through insulation is a conductive heat transfer, there are instances when adding insulation actually increases heat loss.  The thickness at which insulation begins to decrease heat loss is described as the critical thickness.   Since the critical thickness is almost always a few millimeters, it is seldom (if ever) an issue for piping.  Critical thickness is a concern however in insulating wires.  Figure 3 shows the heat loss vs. insulation thickness for a typical insulation.  It's easy to see why wire insulation is kept to a minimum as adding insulation would increase the heat transfer.

ins2.gif (14405 bytes)

Thinking About Insulation from All Sides

   Three major factors play an important role in determining insulation type and thickness.  Here, we'll focus on resolving the thickness issue since many manufacturing facilities have a "standard" type of insulation that they use.  The three key factors to examine are:
1.  Economics
2.  Safety
3.  Process Conditions
    Each situation must be studied to determine how to meet each one of these criteria.  First, we'll examine each aspect individually, then we'll see how to consider all three for an example.

Economics

    Economic thickness of insulation is a well documented calculation procedure.  The calculations typically take in the entire scope of the installation including plant depreciation to wind speed.  Data charts for calculating the economic thickness of insulation are widely available.  Below are links to economic thickness tables that have been adapted from Perry's Chemical Engineers' Handbook:

Table 1: Economic Indoor Insulation Thickness (American Units)

Table 2: Economic Indoor Insulation Thickness (Metric Units)

Table 3: Economic Outdoor Insulation Thickness (American Units)

Table 4: Economic Outdoor Insulation Thickness (Metric Units)

A small, DOS based computer program is also available to help determine economic thickness of insulation.  Download this program here!  (Also available in Software Corner)

Example of Economic Thickness Determination:
   
Using the tables above, assuming a 6.0 in pipe at 500 0F in an indoor setting with an energy cost of $5.00/million Btu, what is the economic thickness?
    Answer:  Finding the corresponding block to 6.0 in pipe and $5.00/million Btu energy costs, we see temperatures of 250 0F, 600 0F, 650 0F, and 850 0F.  Since our temperature does not meet 600 0F, we use the thickness before it.  In this case, 250 0F or 1 1/2 inches of insulation.  At 600 0F, we would increase to 2.0 inches of insulation.
    Economic thickness charts from other sources will work in much the same way as this example.

Safety

    Pipes that are readily accessible by workers are subject to safety constraints.  The recommended safe "touch" temperature range is from 130 0F to 150 0F (54.4 0C to 65.5 0C).   Insulation calculations should aim to keep the outside temperature of the insulation around 140 0F (60 0C).  An additional tool employed to help meet this goal is aluminum covering wrapped around the outside of the insulation.   Aluminum's thermal conductivity of 209 W/m K does not offer much resistance to heat transfer, but it does act as another resistance while also holding the insulation in place.  Typical thickness of aluminum used for this purpose ranges from 0.2 mm to 0.4 mm.  The addition of aluminum adds another resistance term to Equation 1 when calculating the total heat loss:

inseq3.gif (3038 bytes)        (3)

However, when considering safety, engineers need a quick way to calculate the surface temperature that will come into contact with the workers.  This can be done with equations or the use of charts.  We start by looking at another diagram:

ins3.gif (6988 bytes)

At steady state, the heat transfer rate will be the same for each layer:

inseq4.gif (3978 bytes)        (4)

Rearranging Equation 4 by solving the three expressions for the temperature difference yields:

inseq5.gif (1985 bytes)             (5)

Each term in the denominator of Equation 5 is referred to as the "resistance" of each layer.  We will define this as Rs and rewrite the equation as:

inseq6.gif (1249 bytes)                                                         (6)

Since the heat loss is constant for each layer, use Equation 4 to calculate Q from the bare pipe, then solve Equation 6 for T4 (surface temperature).   Use the economic thickness of your insulation as a basis for your calculation, after all, if the most affordable layer of insulation is safe, that's the one you'd want to use.  If the economic thickness results in too high a surface temperature, repeat the calculation by increasing the insulation thickness by 1/2 inch each time until a safe touch temperature is reached.
    As you can see, using heat balance equations is certainly a valid means of estimating surface temperatures, but it may not always be the fastest.  Charts are available that utilize a characteristic called "equivalent thickness" to simplify the heat balance equations.  This correlation also uses the surface resistance of the outer covering of the pipe.  Figure 4 shows the equivalent thickness chart for calcium silicate insulation.  Table 5 shows surface resistances for three popular covering materials for insulation:

inscasi.gif (84044 bytes)

inscover.gif (50744 bytes)

With the help of Figure 4 and Table 5 (or similar data for another material you may be dealing with), the relation:

inseq7.gif (1440 bytes)                              (7)

can be used to easily determine how much insulation will be needed to achieve a specific surface temperature.  Let's look at an example to illustrate the various uses of this equation.

Example of Outer Surface Temperature Determination:
  
Your supervisor asks you to install insulation on a new pipe in the plant.  Recently, two workers suffered severe burns while incidentally touching the new piping so safety is of primary concern.  He instructs you to be sure that this incident does not repeat itself.  The pipe contains a heat transfer fluid at 850 0F (454 0C).  The ambient temperature is usually near 85 0F (29.4 0C).   After checking the supplies that you have available, you notice that you have calcium silicate insulation and aluminum available for covering.  You would like to insulate the 16 inch pipe for a surface temperature of 130 0F.

inseq7.gif (1440 bytes)

Tsurface - Tambient = 130 0F - 85 0F = 45 0F, from Table 5 we estimate a Rs value for aluminum at 0.865 h ft2 0F/Btu. 
Taverage = (850 0F + 85 0F)/2 = 467.5 0F (242 0C), from Figure 1 we estimate a thermal conductivity of 0.0365 Btu/h ft 0F (0.06317 W/m 0C) for calcium silicate insulation.

inseq7a.gif (1848 bytes)
Equivalent Thickness = 6.1 in (155 mm)

From Figure 4 above, an equivalent thickness of 6 in corresponds to an actual thickness of nearly 5.0 in of insulation.

Process Conditions

    The temperature of a fluid inside an insulated pipe is an important process variable that must be considered in many situations.  Consider the length of pipe connecting two pieces of process equipment shown below:

ins4.gif (6115 bytes)

    In order to predict T2 for a given insulation thickness, we first make the following assumptions:
1.  Constant fluid heat capacity over the fluid temperature range
2.  Constant ambient temperature
3.  Constant thermal conductivity for fluid, pipe, and insulation
4.  Constant overall heat transfer coefficient
5.  Turbulent flow inside pipe
6.  15 mph wind for outdoor calculations

inseq8.gif (4821 bytes)               


            (8)

 

 

 

 

 

 

 

 

Another heat balance equation yields:

inseq9.gif (1438 bytes)                         (9)

Setting Equation 8 equal to Equation 9 and solving for T2 yields:

inseq10.gif (1447 bytes)            (10)

Equation 10 provides another useful tool for analyzing insulation and its impact on a process.  Equation 10 has been incorporated into the "Insulated Pipe Temperature Prediction Spreadsheet" available at Software Corner.  You can also download this spreadsheet here.

    One example may be the importance of designing insulation thickness to prevent condensation on cold lines.  Usually, when we hear the word "insulation" we instantly think of hot lines.  However, there are times when insulation is used to prevent heat from entering a line. In this situation, the dew point temperature of the ambient air must be considered.  Table 6 and Table 7 show dewpoint temperatures as a function of relative humidity and dry bulb temperatures.

Table 6: Dew Point Temperatures of Air in Degrees Fahrenheit

Table 7: Dew Point Temperatures of Air in Degrees Celsius

It is crucial that sufficient insulation is added so that the outer temperature of the insulation remains above the dewpoint temperature.   At the dewpoint temperature, moisture in the air will condense onto the insulation and essentially ruin it.

Special Case

For the case of a bare pipe running outside, the chart below can be used to adjust the external heat transfer coefficient from 50 W/m2 K (8.8 Btu/h ft2 °F) to account for temperature difference and wind velocity:

ins6.gif (170589 bytes)

Figure 6: Bare pipe external heat transfer coefficient adjustment

 

Practical Example

ins5.gif (8086 bytes)

    In the figure above, a typical reactor feed preheater (interchanger) is shown.  The heat exchanger resides on the first level of the structure while the reactor is on the second level.  During construction, stream 2 was not insulated because it runs from the exchanger directly to the ceiling away from workers so it posed no safety risk.  The reaction is endothermic, so heat is supplied by a Dowtherm jacket surrounding the vessel.  The equivalent length of the pipe containing stream 2 is 100 meters.  A recent rise is fuel oil costs (which is used to heat the Dowtherm) has prompted the company to search for ways to conserve energy.   With the data provided below, you recognize an opportunity for energy savings.   Any increase in the reactor feed temperature will reduce the reactor duty and save money.  What is the current reactor entrance temperature compared with the entrance temperature after applying the economic insulation thickness to the pipe?

Data:
Calcium silicate insulation
Temperature of stream 2 exiting the heat exchanger is 400 0C (752 0F)
Ambient temperature is 23.8 0C (75 0F)
Mass flow = 350,000 kg/h (771,470 lbs/h)
Rinside pipe = R1 = 101.6 mm (4.0 in)
Routside pipe = R2 = 108.0 mm (4.25 in)
Thermal conductivity of pipe = kpipe = 30 W/m K (56.2 Btu/h ft 0F)
Ambient air heat transfer coefficient = ho = 50 W/m2 K (8.8 Btu/h ft2 0F)
Fluid heat capacity = Cpfluid = 2.57 kJ/kg K (2.0 Btu/lb 0F)
Fluid thermal conductivity = kfluid = 0.60 W/m K (1.12 Btu/h ft 0F)
Fluid viscosity = ufluid = 5.2 cP
Energy costs = $4.74/million kJ ($5.00/million Btu)
Equivalent length of pipe = 100 meters (328 feet)

Calculations:
ins7.gif (9358 bytes)

Temperature difference with insulation is nearly 5 0C.   While this doesn't sound too dramatic, consider the energy savings over one year with the insulation:

Q = mass flow x Cpfluid x temperature difference
Q = (350,000 kg/h)(2.57 kJ/kg K)(5.0K) = 4497500 kJ/h
4497500 kJ/h x 8760 hours/year = 39,398 million kJ/year
39,398 million kJ/year x $4.74/million kJ = $186,746 per year

By insulating the pipe, energy costs have decreased by nearly $187,000 per year

Summary

There are many factors to consider when thinking about insulation.  Insulation save money for certain, but it can also be effective as a safety and process control device.  Insulation can be used to regulate process temperatures, protect workers from serious injury, and save thousands of dollars in energy costs.  One should never overlook it's usefulness.  It's also bad practice to consider only one of the important factors discussed in this article.  The key is to consider all factors that will be affected by installing insulation on a pipe or any other piece of equipment. 