Mahmoud
For tank roof type, you should know the TVP at the max. storage temperature of the tank contents. Based on the local emission regulations, you have to decide on the roof type. For example as per United States EPA CFR 40 Part 60 Subpart Kb:-
- Tanks storing material with TVP’s of 5.2 kPa and less can be fixed roof tanks
- Tanks storing material with TPVs above 5.2 kPa but less than 76.6 kPa must be equipped with external or internal floating roofs or can be fixed roof tanks equipped with closed vent systems with vapor directed to a control device.
- Tanks storing material with TVPs above 76.6 kPa must be equipped with closed vent systems with vapor directed to a control device.
- Tanks storing material with TVPs near atmospheric pressure, should be either API 620 or ASME pressure vessels.
I anticipate heavy fuel oil and diesel to be fixed roof and gasoline to be floating roof type. But you should confirm after obtaining TVPs.
Tank height generally depends upon the soil load bearing capacity. You can obtain that from geotech data. Once you have the height you can work out the diameter based on the working volume. Remember there is a few meters in top and bottom which you need to allow as unused volumes. This is a preliminary way of calculating height and diameter, you have to match these with nominal sizes available from vendors. Generally, this part is handled by the static equipment group.
Hope this helps. I am not an expert in the area but this is what I follow. Comments from Seniors in this forum are welcome.