Hi all
Are there any guidelines/standards for the design of deluge fire water system for Hydrocarbon pipelines?
Let me know if any further information is required.
Thanks in advance.
|
Posted 06 June 2016 - 01:44 AM
Hi all
Are there any guidelines/standards for the design of deluge fire water system for Hydrocarbon pipelines?
Let me know if any further information is required.
Thanks in advance.
Posted 06 June 2016 - 02:19 AM
Pipelines are normally buried and do not require any fire protection / firefighting facilities.
Posted 06 June 2016 - 03:19 AM
ChemiFreak,
Cross-country hydrocarbon pipelines run buried as Dejan has rightly pointed out and need no fire protection.
If you are referring to in-plant hydrocarbon piping which is running across a pipe rack then NFPA 15 provides the guidelines for fixed water spray for fire protection. Clause 7.4.3.7 provides the guidelines for the water spray for pipe racks. Refer the table below for water spray densities for pipe racks as per NFPA 15:
Pipe_Rack_Water_Spray.png 35.9KB 3 downloads
Regards,
Ankur.
Posted 06 June 2016 - 06:15 AM
Thanks Dejan and Ankur.