Black slops flow rate is limited, so that stored quantity never exceeds tank level of 2 m from bottom according to Client, who also requires a steam (3.4 barg) coil close to tank bottom to maintain black slops temperature at 60 0C (viscosity low enough for transfer).
This tank (net capacity ca 14000 m3) will normally contain several layers of liquids from bottom up: mentioned black slurry (not always), water (height not negligible), black and white hydrocarbon liquids of s.g.<1.0. Slops will be carried out by pump through either a floating suction or a normal suction (the latter near tank bottom). Sketch can be seen in attached slops.doc.
Client has excluded naphthas and lighter products, so that total vapor pressure of stored liquid should not exceed 13 psia (limit for floating roof tanks) at 60 0C.
The problem is that an engineering practice document says that storing (and heating) black and white slops together in the same tank is not recommended, due to the risk of boilover / frothover. It is a safety issue. Any advise on the matter or on what is industrially applied for slops would be appreciated. Counter argument from Client is that there are crude floating roof tanks with heating coils .
It is also noted that the floating roof can be stabilized at ~1.1 m from bottom for maintenance, so there should be in this space between: steam coil (plus spare) + series of thermocouples (depth ~1 m from side wall) + probably 2 lateral agitators + nozzles + level sensors etc. Thus black slops measured temperature seems hard to be representative.